How do you prevent thermal shock to a boiler?
If the boiler is hot, can you crack the valve to slowly feed water in?
Just curious.. thanks... any tips are appreciated.
NO! Let it cool down to the point where you can touch the pipes connecting to the boiler. Then feed it slowly.Heaterton said:
Ok thank you. What about when the boiler was recently drained to service something, and it's still hot? Same applies there perhaps?Zman said:If you have a hot water boiler, you should be OK adding water slowly if the circulator is running.
Is this a steam or hot-water system?All Steamed Up, Inc.
Consulting1 -
Just in general. I'm learning the trade. This can theoretically take hours. What does a Tech do while waiting for it to cool? Perhaps do other calls then return if close by?Steamhead said:
(I'm starting as an apprentice soon once I graduate from my HVAC classes. Also just got the "Pumping Away" book delivered tonight.)0 -
Plan your work accordingly. Do the part where you have to drain the boiler first. Then go and do something else on that job, and come back to the boiler.
Or, have the customer shut the boiler down a couple hours before you come.All Steamed Up, Inc.
Consulting1 -
With a hot water boiler if it's hot when you drain it AND you have to drain the system or zone and the work doesn't take a long time (just changing a gauge or something) you should wait to fill the boiler until you can hold your hand on it.
If the system has valves and you can isolate the system or zone and keep it full of hot water while you drain the boiler then when the work is done let the hot zone water into the boiler and feed cold water slowly it will mix with the hot which will warm up the cold water. Run the circulator
It also depends on what you call hot. 130, 140 degrees is probably not an issue if you feed the boiler really slow with cold water. 190-200 degrees is another story1 -
This makes sense. Thank you, I will remember this.EBEBRATT-Ed said:With a hot water boiler if it's hot when you drain it AND you have to drain the system or zone and the work doesn't take a long time (just changing a gauge or something) you should wait to fill the boiler until you can hold your hand on it.
It also depends on what you call hot. 130, 140 degrees is probably not an issue if you feed the boiler really slow with cold water. 190-200 degrees is another story0 -
1st
Why are you draining it?
a cast iron boiler even at 180* empty will cool down fairly quickly so 30 - 60 minutes?
If at 140* when shut down I wouldn’t have a problem slowly adding make up water.0 -
Not draining anything - I'm just asking in general.pecmsg said:1st
I do not want to crack a boiler and I'm curious in how the experts combat this.
From the helpful information in this thread I can say the most important factor here is simply time - I must plan ahead.
If on call, hopefully I can isolate the zones and then flood the boiler with hot water from those zones and then slowly add cold water into the system to bring it up to temp.0 -
Most times, if your replacing parts like a tridicator gauge, air eliminator, extrol tank, relief valve, circulator..., you don't even need to drain the boiler. Just isolate whatever you can, prep your new part(s), drop the pressure to zero, (just drain enough water until the water stops flowing, and close the drain valve before air gets sucked up the hose) and let her rip.
On most residential boilers, your not gonna lose more than 3 or 4 gallons so the cold make up water shouldn't be a concern.1 -
Work fast but use common sense don't get burned0
Thanks guys for the tips, very helpful - working quickly but using common sense...0
- 109 Chimneys & Flues
- 975 Plumbing
- 386 Solar
- 17 Recall Announcements
