IBC Boiler Loud Bang
Trying to diagnose a boiler problem. Boiler is an IBC SL 14-115G3 converted to propane. Have been hearing a loud bang recently and called my plumber who installed it to figure out what the issue was. He guided me to call the gas company to ensure there were no leaks and gas pressures were in spec. Everything was fine on that end. I was able to catch the problem on video the other night and it is posted below. The boiler has only been installed for 3 years and the only other gas appliance I have is a cooktop. Has anyone seen any issues like this? Diagnosis?
https://youtu.be/yBjUeHnYP9U Comments
Another thing to add is that I am unable to replicate the sound. Cranked the heat and sat in the basement for an hour and the boiler did not make the sound. Could not replicate by running hot water either.0
Have they pulled the burner and looked to see if it is intact? Sometimes that mesh screen will sag and cause an issue.0
I had this backfire/delayed ignition on a Munchkin.
The heat exchanger needed cleaning the the drain was mostly plugged.
Cleaned all that and haven't heard it since.
It is exciting if you have the box cover off and are sitting in front of it, I swear it looked as if the cover bulged slightly.0 -
I feel like I have seen posts about this before.0
I have heard it on a Munchkin as well. It was so loud, the neighbors called the police thinking it was a gun shot.
Definitely a combustion problem; perhaps a delayed ignition. Check the gas pressure with a manometer and make sure the pressure doesn't drop by more than 1" wc when it ignites. Also check:
- gas/air mix with a combustion analyzer
- condition of the igniter
- fresh air intake
Call IBC tech. support as a last resort (844) 432-8422.
And let us know the outcome as we all like to learn.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
Just an update on this situation.
Called out the gas company and had them check all the pressures and everything was within spec. No substantial pressure drops. Had them scheduled for a clean and service. After replacing electrodes, cleaning, and replacing the igniter, the sound still persists and is even worse than before. Seems like it is happening every time the boiler ignites now where it was intermittent before.
Will keep everyone posted. Hopefully this situation can be rectified before the winter.0 -
Thanks for letting us know how it's progressing. I'm very interested in what the solution is.
Have you tried calling IBC?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
It is possible the burner mesh has separated. Pull out the burner and check....
Sounds like the fire box has not had all the propane vapors cleared and you are getting a back fire.
You may have a low draft after the boiler shuts down and all the fuel gas or some liquid may be left behind
that causes the banging.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
I always hated working on or servicing propane fired boilers with gas inputs up to 30,000,000 btu's. Give me nat gas, #2, #4, #6 fuel oil any day instead of propane.0
Ahhhhh the plot thickens folks. Boiler is now stuck in standby mode and will not fire to make hot water. COLD SHOWERS THIS WEEKEND!!!! WOOHOO!0
did they do a combustion analysis and set the mixture accordingly?Daannicolar said:Just an update on this situation.
Yes they did. I checked for power at the circulating pumps and my suspicion was correct. They GOT NONE.mattmia2 said: