Beckett oil to gas conversion
Hello,
I want to convert from oil to gas. I have a Williamson OSB-3 steam boiler with a Beckett burner. I stumbled upon the Beckett cg4 gas conversion burner, but unfortunately my boiler is not on the "approved appliance list" for the cg4
Am I out of luck for my particular boiler?
    Steamhead Member Posts: 18,172
    Nope. Use a Carlin EZ-Gas. Where are you located?
    Consulting
  • theONEendONLY
    theONEendONLY Member Posts: 51
    edited July 2021
    Northern NJ @Steamhead
    There are plenty of Steam Guys up that way. Try @JohnNY or @EzzyT .
    Consulting
  • theONEendONLY
    I would like to DIY it, just want to confirm the burner I buy is compatible
    HVACNUT Member Posts: 7,180
    Do you have the proper tools?
    Do you have a manometer?
    Do you have a combustion analyzer?
    Is the meter large enough and is the piping up to code?
    Do you know what else needs to be done besides the burner?
    If the answers to these questions are an astounding "YES!" then go get 'em.
    SuperTech
    Jamie Hall Member Posts: 26,721
    I'll add one more to @HVACNUT 's list. Most jurisdictions require that a licensed plumber or gas fitter certify that the gas piping is correct and tested. Are you qualified to do that?
  • theONEendONLY
    edited July 2021
    I work in the field, but will still consider hiring out. I'm still learning steam boilers.
    What else needs to be done besides the burner?
  • EzzyT
    EzzyT Member Posts: 1,377
    Confirm that the gas meter can handle the additional gas load if not then you’ll need a meter upgrade but also might need a gas service upgrade.
    Draft regulator will need to be replaced with a dual action one, a back draft safety switch installed and wired into the burner.
    A chimney liner might need to be installed if there isn’t already one.
    Replace the combustion chamber refractory along with brushing and clean the combustion chamber and flue passage ways.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Lance
    Lance Member Posts: 328
    In my State in order to do a gas conversion I am required to have a gas conversion burner license. It is the highest in the Master gasfitter license. It grants us the authority to legally modified an existing product. It requires a modification of some appliances for proper overtire draft as well as flue draft. It also takes into account the reduction sizing of the capacity of the firebox combustion chamber. We are taught not all appliances can be converted. Of course those appliance that the mfg. builds for both fuels makes the job a no brainer. Just follow their requirements. Having this training you can design your own heating unit properly. FYI. In some cases a 25-35% reduction in heat capacity is realized. If the old was oversized it could almost always meet the proper existing net heat load.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,584
    Hello,
    Call Beckett, the Williamson water boilers are approved. Same block for both