Low-Loss Header ASME or Non-ASME
space
Member Posts: 3
Hi, when does a low-loss header need to be ASME rated? Thanks
Typically only when ASME items are specified, government work and when you liability insurance covers errors of omission, errors of commission and the insurance company does not have qualified inspectors.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
It is dictated by the BTU rating and design pressure of the system.
Some more details as well as the local codes would help answer the question."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Thanks everyone for the replies
Building is in Saskatchewan Canada, which adopts the National Building Code.
2 condensing boilers (input = 280 MBH each).
Typical boiler pressure (between 12 - 30 PSI).
Low-loss header flow rate is 132 GPM.
Please let me know if you need any more info and thanks again for all the help
you can always build a low loss header with fittings for multiple boiler injection. A 3" header will give you 132 gpm and each boiler will need 2 - 3x1.25 closely spaced tees.
I would question why you need 132 gpm through the header? Sounds high considering the total input.0 -
Closely spaced tees will work.
Yes, the low-loss header is larger than what is needed and we may use a smaller one.
However, I am still unsure when an ASME low-loss header is required.0 -
The provinces are the AHJ. Loss headers are are not required to be ASME in Canada.
Henry0 -
They do need a CRN number. I think if it as the CRN it also has ASME, don't quote me on that.Bob "hot rod" Rohr
Living the hydronic dream0
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 109 Geothermal
- 990 Plumbing
- 389 Solar
