Line voltage thermostats
DaveM
Member Posts: 77
in Oil Heating
Oil fired boiler with hydronic baseboard elements. Two line thermostats two circulators tankless domestic coil with aquastat has a L7224 control. My question is how do I convert to low voltage thermostats
You could use 2 of these https://www.supplyhouse.com/Taco-SR501-4-1-Zone-Switching-Relay
Or 1 of these https://www.supplyhouse.com/Taco-SR502-4-2-Zone-Switching-Relay"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
What is being used as a relay know0
The L2724 is not being used as a relay switch0
Run Low Voltage wiring. Its not that hard!0
Why do you need to keep the line voltage thermostats, if that’s really what you have.
I’m not keeping old line voltage stats I’m replacing with nest smart stats just trying to understand the old wiring at the boiler0
Your post was a little misleading. I understood the post as 2 line (line in this context usually means 120 volt) voltage thermostats, which wouldn’t really be possible, instead of 2-wire low voltage thermostats. Coupled with the fact that you said you want to 'convert' them to low voltage.
Without seeing any pictures, you’re most likely going to have to do what @Zman saidThere was an error rendering this rich post.
I think you will need to give us more info. A quick diagram would help. Do you have 3 wires to the t stats?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
If I understand your original post, you have 2 zones. Each zone is operated by a 120V circulator that is controlled by a 120V thermostat. The boiler has an L7224 aquastat relay that maintains a minimum boiler temperature for Domestic Hot Water (DHW) The fact that the boiler is always hot means that the heating side of the system just needs to turn on the circ pumps to get the heat into the radiators. Although it works FINE it is not the best setup. (FINE as interpreted the way a wife might say EVERYTHING is just FINE)
The problem with that setup is you have no "Priority" for DHW. If you are in the shower and there is a call for heat, the cold water from the radiators will enter the boiler. if there is no Low Limit to stop the circulator(s) from depleting all the boiler water, the DHW temperature may drop to low for comfort. (unless you need to take a cold shower because your wife just said Everything is FINE)
A better way is to use the C1 and C2 terminals on the L7224 control to operate one of the circulator pumps. you do that by connecting the Low Voltage 24V wire to T T on the L7224. This may be a problem with the Nest thermostat, they work better when connected to a common terminal and I don't believe that Honeywell publishes which of the 4 low voltage terminals is Common to the transformer.
So I will suggest a multi-zone relay to control both circulator pumps and using the ZC terminal to provide DHW priority.Edward Young Retired
Here is a diagram you will be able to use. The Switching relay for 2 circulators (Taco SR502 or equal) will provide a way to operate each zone circulator with a Low Voltage thermostat. If your Nest has a problem with insufficient battery charging from a 2 wire setup, then you can try adding a common wire from the thermostat to the switching relay. (see optional green wire on diagram) So run a multi-conductor thermostat wire just in case.
By using the ZC and ZR you will power the burner to the high limit on the call for heat and restrict circulator operation in the event of insufficient DHW, thus giving priority to the DHW.
DISREGARD THE THERMOSTAT CONNECTED TO T T ON THE L7224 CONTROL, IT IS NOT NECESSARY
Respectfully submitted,
Mr.ED
Ed that was extremely helpful thank you so much0
Ed is it ok to connect the taco relay to the L1 L2 on the L72240
Mr Ed can I use the sr503 with the same wiring diagram you showed me thanks for your help0
Update with a little research found out those tstats were originally for electric baseboard heat0
Some wiring help I ran the low voltage wiring to sr 503 besides the L7224 on the boiler there’s an aqua stat on the tankless coil do I need to change that wiring0
- 120 Geothermal