Copper staining from hot water?
dm9321287
dm9321287 Member Posts: 36
edited April 2021 in Domestic Hot Water
I'm wondering if anyone has any ideas what might be causing our domestic hot water to leave blue staining in the sinks/showers?
I understand the blue is copper, and from what I've learned, that's most often caused by either acidic water or bad electrical grounding. I've home tested the water acidity and it's normal, and nothing has changed with the electrical grounding to the mains stop tap under the kitchen sink.
We did have a mains supply pipe leak last year we were unaware of until the massive bill arrived from the supplier, and the blue water started to appear during this time. We've had the pipe replaced with a new plastic pipe, but the blue water continues.
I'm wondering if the water supply might have become contaminated during that time, tipping it slightly to the acidic end, and that's found its way into the copper DHW storage tank?
What's confusing me though, is why is it persisting, if the water is not acidic and the grounding appears to be fine. Could it be that the storage tank is just past its sell by date and slowly corroding? That said, we had it put in when we bought the house about 13 years ago. Is that about right for replacement? Or maybe it's not likely to be the tank at all?
Grateful for any thoughts.
    Jamie Hall Member Posts: 26,842
    The copper staining which you describe is almost always -- not quite, but almost -- because the water is slightly acidic. It doesn't take that much, particularly if the water is also relatively sot.
    So... you describe the pH as "normal" -- but that can be anywhere from 5.5 up to almost 8. What is it? And is the water relatively soft? Or more particularly, softened?
    Larry Weingarten
  • dm9321287
    @Jamie Hall , thanks for the very prompt response. You'll have guessed I said 'normal' because I couldn't remember exactly, but the ph was what it was supposed to be according to the supplier. I'm going to guess 7 but could always easily check again.
    We live in an extremely hard water area and have used the same softener since the day we moved in. So yes, that could well be putting the water on the soft side, but why would the corrosion have become more noticeable now, unless of course, it's been happening all this time and only now become noticeable?
    The combination of slightly acidic water and ion exchange water softening can produce copper staining -- as to why it might have changed recently, haven't a clue. Sorry...
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,010
    Hi, Softening can cause this problem if it’s overdone. You should leave 60-120 ppm of hardness in the water.
    Yours, Larry
  • ratio
    ratio Member Posts: 4,176
    If you went from a metallic service line to plastic, it may be that the bonding isn't as good as you suppose. Even a rusty pipe in the ground is a better grounding electrode than a plastic pipe.
    Canuckerbburdmattmia2
  • dm9321287
    ok, thanks everyone for your input. I am very likely going beyond my very limited expertise here, I thought the water feed was bonded to protect against the pipework being charged, as opposed to providing the earth itself?
    Here in the UK, replacement of water feeds with plastic piping is now standard practice, as the old iron (or worse, lead) pipework put in over a century ago all disintegrates. The bond is to the copper next to the stop tap where the supply enters the kitchen. The mains gas pipe is similarly bonded before it reaches the meter. Both of these earth cables return back to the consumer unit.
    I'd have thought, but could very well be wrong, that even if the water supply pipe is no longer providing adequate earthing itself, the fact it's connected back to the gas pipe (via the consumer unit), would still provide good grounding (assuming there's not another grounding to the consumer unit, which I'm guessing there probably is)?
    All that said, the problem started before the water pipe was replaced and the supply was bonded in exactly the same way (albeit the feed pipe was metal). So is it not most likely something else?
    Noting the comments about the softener, and having retested the water last evening (it's coming up between 7 and 8 ph, so slightly alkaline, if anything), I am completely perplexed. Something is obviously causing copper corrosion in the system, and most likely in the hot water storage tank, given the blue is coming from the hot water (I understand the corrosion is exacerbated when the water is heated).
    The softening level of the softener cannot be adjusted. The whole thing is entirely automatic, and operates kinetically. You put in blocks, it softens as needed. Been doing that for 13 years here, and 4 years in pervious house. Granted, it could be knackered, but I wouldn't say the water is noticeably soft, just not hard.
    I guess one option would be to bypass the softener for a while and let the water harden, so as to see what happens? Would this cause the staining to stop notwithstanding any legacy corrosion within the tank? It would certainly identify the problem if it's the softener.
    Alternatively, would it perhaps be worth trying draining down the hot tank completely and seeing if that removes any corroded sediment that may have occurred through mineral ingress when the supply pipe was failing last year? Or would that more likely make things worse?
    If need be, I'll just swap the tank out (and will discuss with my engineer when he visits again in the next couple of months to service the boiler), but I'd ideally like to get a clearer idea as to whether that's necessary before I go there, or if there might be a simple fix somewhere that could correct this.
    Could it be, for example, as simple as an electrical cable in close proximity to water pipes? We have a lot going on in the system in a couple of places (powering controls and pumps, for example), and whilst all the cables are correctly insulated, is there any way they could be charging the copper pipework somewhere?
    Or is it just that some of the pipework in this old (125 year plus) house is likely knackered?
    Further thoughts very much appreciated.
  • Larry Weingarten
    "I guess one option would be to bypass the softener for a while and let the water harden, so as to see what happens? Would this cause the staining to stop notwithstanding any legacy corrosion within the tank? It would certainly identify the problem if it's the softener." YES!
    Yours, Larry
  • ratio
    Check for bonding jumpers around the water heater & softener, from inlet to outlet. I'm unfamiliar with your style of appliances, but over here a water softener may very well be 100% plastic. if the inlet was 'bonded' via the old water service line, it could be floating now.
  • dm9321287
    edited April 2021
    Thanks again @Larry Weingarten and @ratio for your further input.
    I've taken a closer look at the bonding and I think if anything, that might be the cause. The plastic water mains supply pipe connects to copper, which is bonded. That then connects to plastic and goes off to the softener where it connects to copper, goes through the plastic softener, connects again to copper, then plastic again to come and back to the original copper before going off into the rest of the house.
    I'm wondering therefore, whether the plastic possibly creates the 'floating' bond, i.e. only the kitchen sink (unsoftened) water tap is bonded, and once it connects to the plastic to go to the softener, the earth is lost. That said, when it comes back and connects to the copper to go to the rest of the house, a small run of that copper is in the concrete slab in the kitchen floor, before it goes off under the suspended floors. Could that immersion in the concrete slab be sufficient to earth it from that point on? I'm wondering if that's why it's not re-bonded.
    If the concrete is an insufficient earth, I'm guessing I can bond by connecting the current bonded point to the exiting copper pipework that runs off into the house (bearing in mind that the only accessible pipework I can connect to is the feed to the dishwasher, which tees off from the pipework that runs through the concrete slab)?
    Am I thinking along the right lines here? Thanks again.
  • ratio
    I would think embedded in concrete sufficient grounding to prevent issues, but it likely doesn't meet the code definition of bonding. I'm not familiar with your codes, but over here I'd throw a bonding jumper across every discontinuity in the metallic piping, & verify there's a properly sized jumper in place to the grounding electrode.
    These names are from the National Electric Code & might not line up with the definitions in whatever code you must follow, but the concept should be the same.
    I'm basing all of this on the fact that it started immediately after the old pipe was replaced with non-metallic.
  • dm9321287
    edited April 2021
    Thanks @ratio, very helpful, once again.
    Technically, I believe the pipework is bonded compliant with the UK regs, at least insofar as there is main bonding from the central grounding to the copper pipework immediately after the plastic supply pipe. It was connected here before the supply pipe replacement.
    The staining didn't start after the pipe was replaced. It's been noticeable for some time now, and I thought it might perhaps be linked to the degrading metal supply pipe (once I learned of the leak). In other words, was the degradation of the metal supply pipe somehow increasing the acidity of the water? It seems not, as changing the pipe has done nothing for the staining (but has drastically reduced our water bill).
    Having tested the water myself (not professionally), I don't believe it's acidic, either at the mains or after the softener. Therefore, it must be something else and the only other cause I'm aware of is faulty bonding.
    Given it's apparently compliant with the regs (main bonded and grounded), the only thing I can think is that the bond is lost somewhere after the bonding. The would most obviously appear to be when the pipework switches to plastic to go off to the softener, before switching back to copper after the softener. That subsequent copper work is not therefore bonded (loss of continuity) but as I mentioned, it is initially set in concrete. After that point, I believe it's copper throughout, and importantly, all the way to the indirect hot water cylinder.
    I guess at the end of the day, it's probably a process of elimination, and connecting a bonding jumper from the currently bonded point to the pipework after the softener is easy enough to do and may well solve the problem (unless of course the concrete slab negates the need to do that). If it doesn't, then I am well and truly stumped.
    Thanks again for your help. As I've always found on here, experienced input triggers thought processes that can often take one down the path to a possible solution.
  • dm9321287
    I found the cause of the staining, so I thought I'd post an update in case anyone else is looking to solve this issue in the future.
    A week or so ago, our water got noticeably harder, and it turned out that the blocks in the kinetic softener had got stuck just above the salt platform, so the water wasn't being softened. Nor was the blue staining appearing.
    After pushing the blocks down and reloading the softener, I isolated the softener and then opened the bypass valve a tiny amount (just enough to make the tap in the sink above drip every now and again). I then left the bypass there and reopened the taps to the softener, thereby adding just a small amount of unsoftened water to the system (through the bypass).
    The water feels the same as before (softened) but the blue staining hasn't returned, suggesting that it was indeed the softness of the water all along, that was just enough to tip the pH sufficiently to react with the copper piping. Having now added just a tiny amount of hard water, I've managed to neutralise it and so far, it seems to have worked. If the staining returns, I'll open the bypass a little more and see what happens. Of course, this is because my softener isn't adjustable. I can't set the softness so have had to resort to manual mixing. I suspect it may be on its way out if it's now over-softening.
    Interestingly enough, the home pH tests did not pick up the difference, but then again, I guess they're not that sophisticated and the pH causing the staining was still within the normal, neutral band.
    Thanks again @Larry Weingarten. Without your response I probably wouldn't have thought along these lines.
    Larry Weingarten
  • Derheatmeister
    Derheatmeister Member Posts: 1,659
    It would be advisable to check the incomming waters PH Level before the softener with a calibrated PH pen..
    Aquarium suppliers sell them and they do not cost that much.
    If you incomming water is hard you may try a Scale transformer vs. a water softner which is better for the enviroment and cost less to run/Mantain..
    GMX 800 and Magnetic online.de has devices that work.
    Hope this helps.
    hot_rod Member Posts: 26,604
     most softeners have an orifice on the line for the brine tank that regulates how much brine is drawn in. They are usually stamped to the gpm rate over here.  Is it a timer backwash or demand style meter?  It should only backwash after a certain amount of water has gone thru, not by a timer or you risk over softening.
  • dopey27177
    dopey27177 Member Posts: 916
    When the water main was repaired with plastic pipe the piping system was no longer grounded.
    what you need to do is have a new ground installed from your visible copper pipe to a ground rod outside the house. This can possibly be a do it your self job.
    Years ago I did this in my own home. I used an old piece of 3/4" brass pipe as the grounding rod.
    My guess is you can use a 3/4" copper pipe about 4 feet long as the ground rod.
    Use a green # 12 wire clamped on indoor water supply near the shut off valve and clamp to the ground rod.
    try to get stainless steel pipe clamps, clean the pipe and use dielectric grease on pipe before clamping.
    According to you the only thing that changed in your home was the plastic pipe repair to your water main.
    Jake
  • dm9321287
    Thanks @hot_rod. The softener is metered and if I'm getting my litres to US gallons maths (or math) right, it's 1.479 GPM flow rate - that according to the manufacturer, however, see third para below.
    Thanks @dopey27177 too, although here in the UK a grounding of the mains stop tap is, I believe, a 'Part P Buildings Regulations' requirement. Mine is accordingly connected directly to the household grounding rod along with all the other earth connections in the house. You're right that the only change was the installation of the plastic mains supply pipe, but the staining started before then.
    What may have happened without me being aware, was the softener starting to get a little past its sell-by date (now over 16 years) and maybe now over-softening. I'll see how it pans out. If the staining returns and I have to open up the bypass more and more, it looks like the softener is probably shot.
    Thanks for your thoughts both, much appreciated.