Combustion Air
MR_Cosna
Member Posts: 4
I have a basement that my architect says needs 100sq inches of fresh air. My contractor wants to get the air through the 2 feet by 6inch window next to my furnace. The architect wants to go through the joist.
I am so confused.
how many btu is the FHA furnace?
Makes all the difference.
A furnace, water heater that uses more BTU needs more air for combustion to happen safely.
Are there other fuel burning appliances in the mechanical room?
No just the furnace and hot water tank. I just know that based on square footage and btu of the furnace I need 100 sq inches of combustion airkcopp said:Makes all the difference. A furnace, water heater that uses more BTU needs more air for combustion to happen safely. Are there other fuel burning appliances in the mechanical room?0 -
Your mechanical room must be pretty small
Simple fix would be to either add a couple ( 1 up and 1 down) openings to allow fresh air to come in or use a fan- in- a - can that draws in air when the furnace turns on.
Whether you have the space is not a valid question. You have to have the space, or the appliances will not be safe to use. Your contractor's size window (144 square inches) is technically big enough, but will have to be open at all times when either appliance is running.Br. Jamie, osb
First of all, you have a boiler not a furnace.
There is a name plate on the inside of the boiler door on the right or left side where the fire tubes and gas valve are. The tag will state the input BTUs. Same with the name plate on the water heater.
If you have a clothes dryer in the same place, that makes a difference, too.0 -
The architect has already sized the opening, why ask about ratings?
@MR_Cosna
When he say 100 square inches of opening that means 100 sq inches of free area. So if a louver or screen is installed over the opening the area the louver or screen material takes up must be allowed for.
If you need 100 free area you will need an opening 25%-50% larger depending on the louver.
To keep from freezing pipes you need a dampers system or a "fan in a can" that will only bring in air when the boiler or water heater are actually firing. Doing this requires someone that is farmalier with this. And the damper or fan must be interlocked with those two appliances so they cannot run without combustion air0