Steam boiler overfills and leaks water
Vince1017
Member Posts: 7
Weil McWeil steam boiler. The water level does not appear to remain at a constant level. I always fill it up 1/2, low water level light turns off. I come the next day - everything is ok, I come the day after and see water on the floor next to steam release valve. Water level gauge sometimes shows 3/4. I don't have an auto feeder, how does it overfill? Where do I look?
Sounds like something is wrong. Is it possible that the pressure gauge and the pressure control are not connected to the actual steam pressure because the pressure pigtail is blocked? that would account for the pressure getting high enough to blow the relief valve. But I would think there would be a lot of noise involved
Pictures of the boiler piping from far enough away to see from floor to ceiling
Then close up of the pressure control, the gauge, and the return pipe "Hartford Loop" area. They would be the odd piping design near the bottom of the boiler where the water returns to the boiler
Also a picture of a radiator or two showing the air vent or traps if any.
If you have water on the floor near the pressure relief valve, something is seriously wrong. The boiler should operate on a maximum pressure of 2 psi. The relief valve shouldn't open until 15 psi.
So the first thing to do is to find out if the pressure control on the boiler is operating as it should. Is there a usable low pressure gauge? Probably not... take off the pigtail connection to the pressure control and make sure it is thoroughly clean and clear. Likewise the opening to the boiler. Add a low pressure gauge -- say 0 to 5 psi-- onto it and reattach the pressure control. Set the pressure control to cutout at 2 psi for the moment (be sure you set it correctly; different types are set differently). Fire the boiler and make sure it cuts out at 2 psi, assuming that it does come up to that pressure (it may not).
Now on the water. Water isn't magic. So somewhere there is a pipe or pipes connecting your water supply to the boiler, and the trick is to find out which one is supplying the additional -- and unwanted -- water. It could be the normal feed, with a valve which is leaking. If there is a domestic hot water coil, it could well be that.
I'd replace the pressure relief valve while I was at it -- if it has been opening, it may not reseat properly.Br. Jamie, osb
Sounds like you have a leaky valve on the fill line. What kind of valve is it, and are you filling from a cold water or hot water source?Just another DIYer | King of Prussia, PA
if that pressure relief opens because of high pressure you’ll hear it in the house. It’s loud.0
@Vince1017
Do you have an indirect hot water tank or a tankless heater coil installed on that boiler?0