Clocking a 2# Gas Meter
Zman
Zman Member Posts: 7,610
A while back there was a discussion about adjusting the BTU content of natural gas in a 2# system.
Someone posted a formula that even allowed for a high-altitude adjustment.
I know I saved the darn thing but cannot find it.
Does anyone remember or know the formula?
Albert Einstein
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 698
    (Atmospheric pressure + gas pressure) / base pressure = pressure correction
    Atmospheric pressure = the atmospheric pressure at your location.
    Gas pressure = the gas pressure entering the meter
    Base pressure = the referenced atmospheric pressure that your gas supply company uses. Most of the time this is equal to atmospheric pressure, but sometimes it is not.
    For example, where I live the atmospheric pressure is 14.73. Washington gas uses a base pressure of 14.92.
    So my pressure correction at 2 psi would be:
    (14.73 + 2) / 14.92 = 1.12
    Never stop learning.
    Zman
  • Mike_Sheppard
  • Zman
    @Mike_Sheppard
    Thanks for the follow up.
    This formula checks out with an estimate I made for a spread sheet a few years ago using an actual high and low pressure meter in series. High altitude makes a big difference in the correction factor.
    Albert Einstein
