Is this a main line steam vent of some kind
eagle20mark
Member Posts: 4
Here are some pic's of a piece on the condensate return line,
You need to stand farther back so we can see. That looks like a boiler return trap. The street elbow on top is your air vent. I see some cross over traps.
That is a vapor system. What problems are you having? You have to run that at very low pressure.
Others that know more about vapor will comment @Jamie Hall0 -
I'll comment quite happily -- when I can see more of the system. And get a better idea of what is connected to what...Br. Jamie, osb
Floor to ceiling shots of piping, several sides would be good.0
Might be an air trap rather than a return trap. There may have been a check valve installed in that street 90 to hold vacuum, which worked quite well when the system was coal-fired.
Have you found any manufacturers' info on that unit, or anything else on that system? Where is this system located?All Steamed Up, Inc.
Consulting0