Would shutting off water mess up our VXT feeder?
It won't damage the feeder -- although you would see some really crazy numbers on the display.
What I'd be far more concerned about is ensuring that you have two (2) functioning low level cutoffs on your boiler. Low water cutoffs have been known to fail, on occasion, but rarely. If you have two, then it will be even rarer.
If you don't have two, I'd shut off the boiler or hire someone to come and check the house -- and the boiler -- daily. Cheap insurance.Br. Jamie, osb
We have a probe type LWCO. I certainly wouldn't want to risk the boiler running dry. Can't turn it off in winter, and it is rather isolated so it would be difficult to have someone check on it daily. Maybe the better option would be to leave the water turned on but turn off the well pump. The feeder would have its water supply and in case of a pipe break, we would have a max of 30 gallons of water spilled vs the well pump continuing to flood everything.0
No. The VXT water feeder's internal logic will put the feeder into "lockout" if the boiler fails to fire after two consecutive feed cycles. When you want the feeder to work again, you would just add water yourself and turn the power off and on. Done.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Thanks guys. What I'm doing is turning off well pump but leaving water turned on. That way, feeder still will work and boiler won't shut down due to lack of water. But if we have a pipe freeze or fail, only a limited amount of water will come out before tank is empty. Still quite a bit, but not a massive flood.
On the Hydrolevel website, the literature says no more than 25 gallons per year fresh water for my size boiler (130,000 btu), but on the Supply House website, The VXT installation paperwork says 10 gallons per month.
That's a huge difference. Which is correct?
Neither. On a boiler that size I'd say 1 gallon per month maximum. Any more than that and you should be checking for leaks, steam or water.Don_175 said:Thanks guys. What I'm doing is turning off well pump but leaving water turned on. That way, feeder still will work and boiler won't shut down due to lack of water. But if we have a pipe freeze or fail, only a limited amount of water will come out before tank is empty. Still quite a bit, but not a massive flood.
That's a huge difference. Which is correct?0 -
"correct" is a difficult word here but I would say more like 1 gallon a month during heating season. It could be less.
The concern is if you have any steam or condensation leaks, you can use quite a bit more than that.
Honestly if you are going to be there on weekends, I wouldn't be too concerned. Fill it up to half way up the gauge glass and mark the level, then see where it is next weekend.NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el0