What are all the causes that will make a pressure relief valve trip on Steam Boiler?
Dairon421
Dairon421 Member Posts: 81
Just wanted to know so when I go on a service call I can check everything.
    pecmsg Member Posts: 6,781
    What formal training have you had?
    a short list of special tools?
    Jamie Hall Member Posts: 26,838
    edited February 2021
    Root causes? Or just cause? The two proximate causes are first, and overpressure in the boiler. Second, a faulty valve.
    But if you are facing the first proximate cause -- an overpressure in the boiler which actually trips the pressure relief valve -- don't even think about the valve. You are going to have to find out why the pressure control device didn't trip or, if it did trip, why it didn't shut down the boiler. And that is a subject for a small book.
    EBEBRATT-Ed Member Posts: 19,586
    Bad pressure control, or one set to high. Plugged pigtail or plugged boiler connection
    or bad safety valve
  • bburd
    bburd Member Posts: 1,245
    Burner primary relay contacts stuck closed. Extremely rare, but it happens.
    Bburd
    mattmia2 Member Posts: 15,600
    Note that if the relief valve blows on a steam boiler because it is over pressure, it usually is very violent, once that pressure is released the entire contents of the boiler is now superheated and can almost instantly all flash in to steam which can burn your skin or the inside of your lungs.