Is it NFPA 211 that covers solid fuel boilers? Are their EPA requirements in play now for emissions. @Bob Harper anyone up to speed on code requirements for placement, venting, etc?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream

Comments

  • Zman
    Zman Member Posts: 7,614
    Not sure about NFPA, In Colorado, lot's of regs have popped up at the local level. Most areas require EPA 2 cert and distance to neighbors or minimum lot size.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • leonz
    leonz Member Posts: 1,932
    edited February 2021
    Hello Bob,

    NFPA 211:

    "Standards for chimneys, fireplaces, vents, and solid fuel burning appliances".

    The forest eaters especially (outdoor wood boilers/water stoves) have come under a lot more regulation and limitations in their allowable locations with regard to zoning.
  • hot_rod
    hot_rod Member Posts: 28,288
    I guess I may need to buy a download of 211 to get some answers, thanks.
    Feel free to contact me with that other question on the buffer idea. PM me here or bob.rohr@caleffi.com
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • PC7060
    PC7060 Member Posts: 1,955
    @hot_rod - what did you come up regarding the combustion analyzer?  I saw a nice used Testo 320 recently.  I believe the 320 has user replaceable CO sensor which would be good since I would only be using occasionally. 
  • hot_rod
    hot_rod Member Posts: 28,288
    I'm leaning towards the Wohler 450. Touch screen, ap, everything on a single screen, no scrollong around for the different readings Found them for 1287 at test instruments
    https://www.youtube.com/watch?v=3BdpmXCxRZU
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    PC7060
  • Bob Harper
    Bob Harper Member Posts: 1,187
    edited February 2021
    211 is just for combustion venting. You can view it for free online here: https://www.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=211
    Solid Fuel-fired boilers are listed under UL 2523. Neither of these stds. cover emissions or efficiency. Here is from the EPA: https://www.epa.gov/residential-wood-heaters/fact-sheet-summary-requirements-wood-fired-hydronic-heaters . Here is an article that does a good job explaining some of the difficulties with efficiency testing of solid fuel fired boilers: https://woodboilers.com/wood-boiler-efficiency-and-epa-ratings/ . Meanwhile, a growing number of jurisdictions are outlawing them. You can also contact the Hearth, Patio, and BBQ Assn. in Arlington, VA and talk with their Gov't Affairs head, John Crouch. HPBA.org
    HTH !
    PC7060
  • hot_rod
    hot_rod Member Posts: 28,288
    Trying to find out what the code states about a locating a wood fired boiler in a shop or garage.
    Absolutely no? Or sealed combustion allowable? Or 18" above the floor was once allowed.
    Bob "hot rod" Rohr
    trainer for Caleffi NA