Boiler does not stay lit
Flightmedic911
Member Posts: 8
Just finished installing a new system. I'm running a 120,000 btu Noritz 661 NG DV. I believe I have all the air out of the lines and system. The boiler fired up and ran quiet for about 30 min. Raised the line temp by 10 degrees F. The boiler flame then shut down, but the display indicator shows fluid flow still but the burner does not light. It has no error codes. Any thoughts? Does it have a duty cycle?
what were the numbers from the combustion analysis?0
Sorry for my ignorance. I have no idea what you are referring to.0
If it helps, when it runs I have a very clean blue flame, no dead spots, no flickering.0
The ignorance is ours. Who exactly installed the boiler? And do they have any boiler experience?
If you installed the boiler and have zero experience, then I don't believe you'll get advice on combustion adjustments. I qualified tech is needed.0 -
Products of Combustion cannot be seen. A complete combustion analyses is required.Flightmedic911 said:If it helps, when it runs I have a very clean blue flame, no dead spots, no flickering.
Get your oil supplier out to set up that "System" properly!0 -
Oil or gas?0
NG0
I have contacted my HVAC tech. Problem is he is about 2 weeks out because of no heat problems for other customers. Normally we work together and troubleshoot but he is a bit busy.0
Who installed the boiler?0
The OP
Just finished installing a new system. I'm running a 120,000 btu Noritz 661 NG DV. I believe I have all the air out of the lines and system.0 -
Inlet and exhaust are clear.Just to clarify I am only looking for simple things to check before I waste his time. Something that I may have overlooked. I don't screw around with gas0
I have no problem with a Homeowner doing some of the work but always advise before starting let me be there to do the actual start up. I WILL see things that you will miss.0
It was new construction. I ran 1" underground line from the meter to the barn, about 45-50 feet. Ran 3/4" black pipe from just inside the building to the heater, an additional 8'.The venting is about 1' inlet and 3' exhaust, so very short. I will double check the vent for frost, the fan seems loud. Thank you for assisting.0
The screen on the pressure reducing valve or something in the boiler? Is it a new PRV?0
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 109 Geothermal
- 986 Plumbing
- 389 Solar
