flue gases with old CI rads on conventional gas boiler

kensheets2
Member Posts: 36
Hello
I understand that with low water temp installations such as radiant floor heating, return water temps will naturally be less than ideal. My question is if I am running an application using old cast iron rads with a conventional gas boiler and running water around 170-180 will I realistically still need to be concerned with low return water temps in relation to flue gas condensation?
Thanks
Ken
I understand that with low water temp installations such as radiant floor heating, return water temps will naturally be less than ideal. My question is if I am running an application using old cast iron rads with a conventional gas boiler and running water around 170-180 will I realistically still need to be concerned with low return water temps in relation to flue gas condensation?
Thanks
Ken
0
Comments
-
Probably not. The concern arises when the return water to the boiler drops below about 140 -- and stays there -- while the boiler is running. Mostly a control issue. Make sure the boiler is set to hold a source temperature high enough, and to make sure there is enough circulation.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 425 Carbon Monoxide Awareness
- 108 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 963 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements