1 pipe steam wet return line not getting hot
The back 1/3 return line of the house does eventually get hot, but takes an extremely long time, about an hour.
Any help with this is appreciated
TIA
Wet return? Along the floor? The only reason it would get even warm is if enough hot condensate got into it. And, of course, condensate is supposed to get in there -- but enough to get it hot? Slightly warm perhaps, if it takes the condensate from a lot of radiators...
Suppose you have a radiator putting out about 10,000 BTUh. That works out to a bit over a gallon per hour of condensate. That will just barely fill a 2 inch pipe 10 feet long -- during which time it is mixing with the water in the pipe and cooling. It might -- if the return is only ten feet long -- get up to 120 or so... in an hour...
Why do you think this is a problem?Br. Jamie, osb
If I were to want to put a hydronic loop off the return line and maintain it with a aquastat at 140 degrees, then wouldn’t the return line need to be able to reach that temp?0
This idea comes up from time to time, and it does sound attractive. Unfortunately, it doesn't work. There simply is very little -- by comparison -- residual heat in the condensate from steam systems.deebster190 said:If I were to want to put a hydronic loop off the return line and maintain it with a aquastat at 140 degrees, then wouldn’t the return line need to be able to reach that temp?
Go back up to my calculation above. We found there was perhaps a gallon of water per hour. That's around 8 pounds of the stuff. If we suppose that that condensate, when it left the radiator, was at 200 F, and that by the time it got back to the boiler it had cooled to 100 F -- a delta T of 100. That's 800 BTUh that that condensate will give you.
Which is about the same as a couple of hundred watt bulbs.
It's perfectly possible to put a hot water loop running off the boiler in the basement -- but not using the condensate.Br. Jamie, osb
That one degree of change from steam at 212 to water at 211 contains a lot of heat energy. The water going from 211 to room temperature doesn't contain very much. It's not that much water and there is a lot of cold water and pipes in a wet return for it to mix with.
Thanks all for your help and advice. Gonna put the loop through the boiler and put an aquastat on the loop.Would you put it on the supply or return side and at what temperature?0
You should use a tapping as low as possible on the boiler for the supply, and pump away from that. The return line can go -- and perhaps should -- into the wet return.
The aquastat setting -- which would be on the supply line -- should be whatever it takes to heat the space to the temperature you want with the radiation you are using.Br. Jamie, osb
The lowest tapping? There's not always a choice, but I'd take a higher tapping than the lowest to minimize the mud getting sucked through the pump.
Here's how to do it: https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/NJ Steam Homeowner.
Well, true on the mud -- but whatever tapping is used, it must be low enough to ensure that the pump always has a decent net positive suction head on it.ethicalpaul said:The lowest tapping? There's not always a choice, but I'd take a higher tapping than the lowest to minimize the mud getting sucked through the pump.
Here's how to do it: https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/Br. Jamie, osb
I agree. Question: can you tap from a bit higher (but still well under waterline of course) and then run it immediately down to the floor to get that additional head on it?
Yes -- that works fine.ethicalpaul said:I agree. Question: can you tap from a bit higher (but still well under waterline of course) and then run it immediately down to the floor to get that additional head on it?