Hello,

I'm in the process of designing a boiler system and due to limitation of budget I can only go with a Navien NFB-200 as opposed to its comparably sized Viessmann boiler. I have used the Viessmann low loss header 80/60 before and really like the product. Wonder if this low loss header is compatible for other boiler brands? If not, I would have to go with the Caleffi SEP4.

Thanks!

Comments

  • Ironman
    Ironman Member Posts: 7,376
    Options
    Have you done a heat loss calculation? 200k btu is very large boiler. The average sized home needs less than 50k btus.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Ironman
    Ironman Member Posts: 7,376
    Options
    The Caleffi Sep4 will work with any boiler that needs a LLH.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • ChickenSoup
    ChickenSoup Member Posts: 2
    Options
    Ironman said:

    The Caleffi Sep4 will work with any boiler that needs a LLH.

    Thank you! 3 floors in house in which one is on an uninsulated slab. Big house. My heat loss calc is oversized and came out to about 140k BTUs for the house. Didn't look at the size of the current boiler but it sure is a big mod con. Greatly appreciate your input.
  • TAG
    TAG Member Posts: 755
    Options
    I used the Viessmann on my new system with the Viessmann boiler .... frankly ... the Caleffi looks nicer.