Zone Valve
clutch
clutch Member Posts: 3
edited December 2020 in THE MAIN WALL
Can I hook up a end switch on a zone valve to run 2 relays
    EdTheHeaterMan Member Posts: 11,575
    Yes and No
    You may need to have a single pole double throw relay to isolate the relays you are operating.
    Once the end switch pulls in both relays, the coil resistance of the relay may be enough to create a holding circuit that will not allow the other relay to disengage when the end switch opens. (or both relays could get the transformers fried by making 48 volts)
    EDIT:
    It would be best to isolate the relays. Especially if the relays are operated by different transformers End switch to pull in the SPDT DPST relay and the separate poles of the SPDT DPST relay operate the final relays without cross-connecting the wiring or
    Need a diagram? Let me know the model number of the relays you want to operate and I'll see what I can come up with.
    STEVEusaPA
  • clutch
    May need or do need?
  • clutch
    Thank you
    depends on the application.
    HVACNUT Member Posts: 7,234
    Also what is the power source? Can it handle the contact ratings?
    Jamie Hall Member Posts: 26,842
    The end switch is just that: a switch. It won't power anything. What it will do is complete a circuit from an appropriate power source through your relay -- or relays -- to energize them. Then, of course, you can do pretty much what you want with the relays.
    hot_rod Member Posts: 26,604
    Most zone valve switches are rated for 120V, a 1A. As long as the "loads" your are switching are powered by the same circuit you should be fine.
    I think Ed means a single throw, double pole relay that would isolate two different circuits or load, as an on/ off function. And depending on the isolation relay it could have a higher current rating than the end switch.
    We need to know more about what you are trying to control or switch.
    Thanks for catching my error @hot_rod. That was a case of "Do
    What I Mean, Not What I Say"
    Here is an example of what I mean
    Isolation DPST relay isolates the ZV end switch from the transformers on the individual transformers of the 2 "object" relays Illustrated by 3 different color circuits.
    Although I can't see a practical use for this particular diagram
    Still interested to know what @clutch's application is!!!