Location of Main Vents - Not End of Main or Return
Ps44
Member Posts: 30
I was reading a brochure from
Peerless Boilers and was surprised to see that they said you should not locate the main vents at the end of the main or return since all my main vents are located exactly that way. I was wondering if anyone could enlighten me why the dead men would locate them there and Peerless is saying they shouldn't be. Pictures from brochure above and a main vent below. Any thoughts would be welcome to understand this better.
It is certainly preferred that they be set back from the end of the main or return, but it makes little difference to the venting -- and as @Hap_Hazzard said, rather forcefully, if things are done correctly there won't be a water hammer threat.Br. Jamie, osb
The 90 on the end of the main does add a little protection.
But they had a take off where the vent should have been, so it was a compromise for that day.
What you can do to get the protection is remove your vent, add a 6" or more riser with a 90, then a 12" horizontal pipe with another 90, then a riser as space allows for your vent.
This gives enough restrictions that may help with water hammer.0 -
what you can do,
at least with that vent pictured,
is to raise the vent up on a nipple and coupler, like in the "approved" drawing,
or 90 or 45 away and add a nipple and same angle, and raise the vent up,
or even build an antler if you're finding you need more venting capacity.
you're moving the vent up and away from any condensate water flow at those end of mains.
known to beat dead horses0 -
I strongly agree with raising the vent as high as possible. I would use 45s for any offset as a horizontal pipe could be pitched the wrong way and hold water
Vents on a tee at the end of the main or dry return if they don't spit water and work ok just raise them and leave them in the same location0 -
Sorry I didn't say this but I don't have a water hammer problem or any problem at all so this was definitely done correctly. I was just being curious about the differences. Thanks for all who weighed in.0
I just don’t think it’s an issue unless you have wet steam and hammer issues. The trickle of condensate in most systems should never blast out a vent unless the system is out of whack.
A 200k boiler output is 160k BTU. That converts to approx. 2.7lbs of water or 0.3 gallons per minute of condensate. Thats a steady trickle. That will fill a pint glass in 22 seconds.
The piping was probably good 100 years ago. It’s the 40 years ago to present stuff you have to watch out for.I assume your boiler isn’t over 100 years old?