Pump size
Snowmelt
Member Posts: 1,457
I have 700 feet of linier piping 30 elbows , 4 tees. Starts off with two inch pipe for 120 feet then goes to 1-1/4 and total btu lose of building is 220,000 btu, what size taco pump?
It’s a section of a school
Just just using some quick rule of thumb, you’d probably have about 40’ of head @ 22 gpm. Your head may be somewhat lower due to the section of 2” pipe involved. Is it iron or copper pipe?Bob Boan
A Taco 2400-50 may come close.
If you contact them, they can size it for you.Bob Boan
All copper piping0
This is from my "GoTo" book on the subject.
Look at the section second from the bottom "PUMP HEAD"
If that is the only pump on the system, that formula works. If it is a zone off of a central boiler that does more than just the section you described, then you add 33% to the total equivalent length for the piping from the boiler to the zone That is on page 13 of this:http://media.blueridgecompany.com/documents/ZoningMadeEasy.pdf
But you will want to read page 7 first to get the whole picture.Edward Young Retired
Bet bet is a B & G system sizer you can calculate it yourself. You can get a B& G wheel or go online and download the app.
If the 700 feet of pipe one way or out and back?0
- 121 Chimneys & Flues
- 15.8K Strictly Steam