Pump size
Snowmelt
Member Posts: 1,425
I have 700 feet of linier piping 30 elbows , 4 tees. Starts off with two inch pipe for 120 feet then goes to 1-1/4 and total btu lose of building is 220,000 btu, what size taco pump?
It’s a section of a school
It’s a section of a school
0
Comments
-
Just just using some quick rule of thumb, you’d probably have about 40’ of head @ 22 gpm. Your head may be somewhat lower due to the section of 2” pipe involved. Is it iron or copper pipe?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
A Taco 2400-50 may come close.
If you contact them, they can size it for you.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
All copper piping0
-
This is from my "GoTo" book on the subject.
Look at the section second from the bottom "PUMP HEAD"
If that is the only pump on the system, that formula works. If it is a zone off of a central boiler that does more than just the section you described, then you add 33% to the total equivalent length for the piping from the boiler to the zone That is on page 13 of this:http://media.blueridgecompany.com/documents/ZoningMadeEasy.pdf
But you will want to read page 7 first to get the whole picture.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Bet bet is a B & G system sizer you can calculate it yourself. You can get a B& G wheel or go online and download the app.
If the 700 feet of pipe one way or out and back?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements