Taco ZVC506 zone control

Grallert
Member Posts: 969
This may be an easy question to answer. Will a taco zone valve control operate both taco and honeywell zone valves on the same system? In other words four taco power heads and two honeywell power heads. A friend asked me this and honestly I don't recall. It's been a few years since I last installed a taco control.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0
Comments
-
It should be , Taco heat motor is a higher amp .9 than Honeywell .3 amp . Check the VA of the transformer in the control . Say you are using 6 Honeywell zone valves . 24V x.3amp =7.2 VA , 7.2 VA x 6 = 43.2 VA needed . I would like to see a 50VA or higher transformer in the 6 zone control .
There was an error rendering this rich post.
1 -
Thanks Ed that was my thought .
I'll make a visit and have a look. Seems that here should be enough to operate the power heads. Some has installed a new 506 and then later another 502 because they felt the 506 wasn't enough. Thank you for the replyMiss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
-
I find myself constantly recommending Taco products for this exact reason.Dave H_2 said:The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va
The SR 506 switching relay for circulators only has a 20va transformer
Dave H.
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
Dave H_2 said:
The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va
The SR 506 switching relay for circulators only has a 20va transformer
Dave H.
I couldn't agree more! Thanks Dave.Zman said:Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
Reverse return and a auto circulator if your building that beast...
There was an error rendering this rich post.
0
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 110 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 977 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements