Taco ZVC506 zone control

Grallert
Member Posts: 561
This may be an easy question to answer. Will a taco zone valve control operate both taco and honeywell zone valves on the same system? In other words four taco power heads and two honeywell power heads. A friend asked me this and honestly I don't recall. It's been a few years since I last installed a taco control.
0
Comments
-
It should be , Taco heat motor is a higher amp .9 than Honeywell .3 amp . Check the VA of the transformer in the control . Say you are using 6 Honeywell zone valves . 24V x.3amp =7.2 VA , 7.2 VA x 6 = 43.2 VA needed . I would like to see a 50VA or higher transformer in the 6 zone control .
There was an error rendering this rich post.
1 -
Thanks Ed that was my thought .
I'll make a visit and have a look. Seems that here should be enough to operate the power heads. Some has installed a new 506 and then later another 502 because they felt the 506 wasn't enough. Thank you for the reply0 -
-
I find myself constantly recommending Taco products for this exact reason.Dave H_2 said:The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va
The SR 506 switching relay for circulators only has a 20va transformer
Dave H.
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
Dave H_2 said:
The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va
The SR 506 switching relay for circulators only has a 20va transformer
Dave H.
I couldn't agree more! Thanks Dave.Zman said:
I find myself constantly recommending Taco products for this exact reason.Dave H_2 said:The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va
The SR 506 switching relay for circulators only has a 20va transformer
Dave H.0 -
Reverse return and a auto circulator if your building that beast...
There was an error rendering this rich post.
0
Categories
- 120.9K All Categories
- 83.8K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 416 Carbon Monoxide Awareness
- 36 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 116 Geothermal
- 154 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 754 Plumbing
- 5.3K Radiant Heating
- 358 Solar
- 13.9K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 37 Industry Classes
- 70 Job Opportunities
- 14 Recall Announcements