Taco ZVC506 zone control

This may be an easy question to answer. Will a taco zone valve control operate both taco and honeywell zone valves on the same system? In other words four taco power heads and two honeywell power heads. A friend asked me this and honestly I don't recall. It's been a few years since I last installed a taco control.

Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,076
    It should be , Taco heat motor is a higher amp .9 than Honeywell .3 amp . Check the VA of the transformer in the control . Say you are using 6 Honeywell zone valves . 24V x.3amp =7.2 VA , 7.2 VA x 6 = 43.2 VA needed . I would like to see a 50VA or higher transformer in the 6 zone control .

    There was an error rendering this rich post.

    Grallert
  • Grallert
    Grallert Member Posts: 833
    Thanks Ed that was my thought .
    I'll make a visit and have a look. Seems that here should be enough to operate the power heads. Some has installed a new 506 and then later another 502 because they felt the 506 wasn't enough. Thank you for the reply

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • Dave H_2
    Dave H_2 Member Posts: 593
    The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va

    The SR 506 switching relay for circulators only has a 20va transformer

    Dave H.

    Dave Holdorf

    Technical Training Manager - East

    Taco Comfort Solutions

    ZmanGrallertSTEVEusaPA
  • Zman
    Zman Member Posts: 7,611
    Dave H_2 said:

    The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va

    The SR 506 switching relay for circulators only has a 20va transformer

    Dave H.

    I find myself constantly recommending Taco products for this exact reason.

    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    GrallertSTEVEusaPA
  • Grallert
    Grallert Member Posts: 833
    Dave H_2 said:

    The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va

    The SR 506 switching relay for circulators only has a 20va transformer

    Dave H.

    Zman said:

    Dave H_2 said:

    The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va

    The SR 506 switching relay for circulators only has a 20va transformer

    Dave H.

    I find myself constantly recommending Taco products for this exact reason.

    I couldn't agree more! Thanks Dave.

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • Big Ed_4
    Big Ed_4 Member Posts: 3,076
    Reverse return and a auto circulator if your building that beast...