Taco ZVC506 zone control
It should be , Taco heat motor is a higher amp .9 than Honeywell .3 amp . Check the VA of the transformer in the control . Say you are using 6 Honeywell zone valves . 24V x.3amp =7.2 VA , 7.2 VA x 6 = 43.2 VA needed . I would like to see a 50VA or higher transformer in the 6 zone control .
Thanks Ed that was my thought .
I'll make a visit and have a look. Seems that here should be enough to operate the power heads. Some has installed a new 506 and then later another 502 because they felt the 506 wasn't enough. Thank you for the replyMiss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
I find myself constantly recommending Taco products for this exact reason.Dave H_2 said:The ZVC406 zone valve controller for all brand zonevalves has two 40 VA transformers in it = 80va
The SR 506 switching relay for circulators only has a 20va transformer
Dave H.
Albert Einstein2 -
Dave H.
Dave H.Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
Reverse return and a auto circulator if your building that beast...
- 117 Geothermal