Design of Electric steam boiler
Hello guys
I would like to ask, if any of you know how to design electric steam boiler. Outlet temperature of steam should be around 700 °C, steam flow 40 kg/h and working pressure is 1,5 bar. I would appreciate any advice on thermal or hydraulic calculation.
Thank you very much
  • ChrisJ
    ChrisJ Member Posts: 17,350
    1300f steam!
    Jamie Hall Member Posts: 27,319
    What are you doing? That's a lot of superheat you are asking for.
    The steam flow is not really that large, relatively speaking, and your pressures are low, so your feed pump doesn't have to be much.
    I would suggest you use a two stage design, the first stage being the steam generator -- around 30 KW or so heating elements (check that -- that's a back of the napkin figure) and a second, superheat stage. That stage is going to require some close attention to the aerodynamics of steam flow, as well as the design and geometry of the heating elements (never mind sourcing them -- elements capable of operating at that temperature are not all that common).