Main Vent Stuck Against Joist
ceilinginway
Member Posts: 2
Hello, Looking for ideas on how to replace this old ventrite 35 main vent that is sitting against the joist. How to get the vent off and then what kind of setup to replace it with? This is on a 2” 33 ft long main off the right side of the boiler.
thanks for any tips!
Remove the nipple or fitting from below0
It appears to be in the wrong place on the steam line. It should be at the end. These main vents should be allowing the air to escape without resistance from the whole length of pipe.
If your pipe returns to the boiler, and drops down to the floor, then it should be there. If the supply pipe rises up from the boiler to the last radiator, then the main vent must be after the last radiator on the line.--NBC0 -
and once you do that, you can use three nipples and two elbows to offset the new one from the joist.STEAM DOCTOR said:Remove the nipple or fitting from below
This is very helpful. Thanks for taking a look at this.
you could replace that 45 with a 45, nipple, and coupler or street 45 and coupler to make it vertical further out from the joist.0