TRV
tobrien02382
tobrien02382 Member Posts: 17
edited October 2020 in THE MAIN WALL
Hi I’m brand new so please excuse me if this is a dumb question.  Do I have to have a vacuum breaker on a TRV on a one pipe steam radiator?   I installed TRVs but they don’t have vacuumed breakers so now I’m wondering if that’s why They’re not working.
Tricia
  • ChrisJ
    ChrisJ Member Posts: 17,068
    Mixed opinions on this.
    I really don't know how much it matters but venting speed matters, a lot.
    You need the venting speed to be close to correct so that the rooms heat properly without the trv.  If you vent too fast it will always overheat trv or not.
    What are you using to control the boiler?  If it's a thermostat which one?
  • tobrien02382
    An oldish Honeywell digital wall thermostat
    Tricia
    Jamie Hall Member Posts: 26,833
    May I presume that the TRV is on the vent? With a very small number of exceptions, vents will not hold a vacuum. A closed TRV, however, will. Since it is unlikely that all the TRVs -- never mind the main vents -- will be closed at once, however, you will get air into the radiator when the system shuts down, whether there is a vacuum breaker on the vent or not. So I'm not sure, either, whether one is needed or not.
  • tobrien02382
    Both of your feedback has been very helpful.  I think at this point I’m going to start looking at the pressure of the boiler as it sounds the TRVs may be ok.  PS they’re working but Rads are just getting super hot while even sets on “1”.
    Tricia
  • motoguy128
    motoguy128 Member Posts: 393
    I don;t have TRV’s on mine. They all seem to work fine. I have TRV’s on 5 Radiators out of 16 total.
    I did add a vacuum relief on the end of the Main vent antler Because Barns and Nobles don’t open under vacuum and my vapor system with its oversized 3” main dropped into vacuum so fast and hard the vents all whistled loudly.
    I agree with others the hte vent rate needs to still be fairly close to correct. So a Maid o Mist straight vent can be used. OR use the included vent which is same vent rate as a Hoffman 40, or about a 4.5 Gorton/MoM.
    However, a TRV without a vacuum relief will allow a radiator to keep heating during a call cycle to the point where it was vented to. So if it’s heated 1/2 way, it will keep heating 1/2 way. However, it should still work as the other radiators will continue heating more and more and getting proportionally more steam in the meantime. So it acts as Radiator size limiter.
    TRV’s work best upstairs and in unused rooms you want only minimal heat in, far from the thermostat.
  • tobrien02382
    Ok so after a bit more research I believe a vacuum breaker is built into the Danfoss valve body I'm using. So that being said. The radiator that is causing me the most problems (overheating). Is heating up even with the TRV turned all the way down to the snowflake setting (the off setting).
    Tricia
  • ChrisJ
    Take a straw.... or a can of air, and blow into the vent while the radiator is cool.
    See if anything changes after that.
  • tobrien02382
    I will try that. Thank you.
    Tricia
  • What sort of main venting do you have? What is your pressure?
    The air in the system should be able to escape with less than 2 ounces, of backpressure, verified by a good low pressure 0-3 psi gauge.
    If your system is not balanced, with steam able to arrive at each radiator simultaneously, the TRV’s will be an ineffective bandaid.—NBC
    Alan (California Radiant) Forbes Member Posts: 4,640
    edited November 2020
    As I understand TRV's on steam radiators, the sequence of operation is as follows:
    - Before the boiler turns on and the system is cold, the vent on the TRV is open.
    - When the boiler is steaming, air is vented out of the radiator vent, allowing steam to enter the radiator.
    - When steam hits the vent, the vent closes.
    - When the room temperature reaches the setpoint temperature of the TRV, the TRV closes, preventing air from going in or out of the radiator via the vent.
    H O W E V E R
    If the boiler continues to steam and the pressure remains constant, steam will continue to enter the radiator, possibly and probably overheating the room. The TRV is only controlling the vent. In order for the TRV to be effective, the boiler has to turn off and the pressure reduced to zero. Once the boiler turns on again and steam tries to fill the radiator, the vent will be open, but the TRV will be closed because the room is warm; steam will not enter the radiator and the room will not overheat.
    Danfoss says:
    The venting action occurs during each system (boiler) on-cycle only when heat is required. Air will re-enter the radiator during the system off-cycle...."
    and
    Boiler/steam supply must not run at constant pressure. This
    prevents the ability for air to enter back into the system.
    So, you have to have an "off-cycle" where the pressure will drop and air is allowed to enter the radiator.
    BTW, I am a steam novice and have only installed one such TRV system on steam.
  • Right on track Alan.
    Additionally, the placement of the thermostat is important as well. Where is yours, and is it configured for steam?—NBC
  • JohnNY
    JohnNY Member Posts: 3,341
    Exactly, @Alan (California Radiant) Forbes.
    TRVs aren't always the plug-n-play device we want them to be. There is always a pressure consideration to....consider. But most of all, they need some good standby time in a heating cycle in order to work well. Let the system take a breath and the TRVs will do their job. To get that to happen, make sure the thermostat you're using has an anticipator setting or a cycles-per-hour (CPH) option that you can set for 1 or 2. Keep the pressure low and give the TRVs a day or two after making changes to allow them to react to a few fresh heating cycles. It's a process.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • tobrien02382
    Nicholas - I don't know what I have for a main vent. I'm going to go down to the basement today and take a few pics. As I also don't know what pressure the boiler is set at. But suspect it is too high. And I totally agree with the fact that my system is not balanced. Baby steps for me. Thank you!
    Alan - That is the understanding I have as well on how TRVs work. I believe the pressure is too high at my boiler
    Johnny - I did want the TRVs to be plug and play and now understand that I should have balanced my system first. I doubt my thermostat has a CPH option as it's from the 90's so I will be reading up on that today.
    I am about to move to a different room in my house.
    Tricia
    That's one way to deal with it. ;)
    EdTheHeaterMan Member Posts: 11,564
    Nicholas -
    Are you bringing your computer with?
    If not, will you come back and visit someday?
  • Zman
    Zman Member Posts: 7,611
    You could always try the high tech approach and through a blanket over the radiator. Maybe not the best solution long term but easier than moving to another room.
    Albert Einstein
    tobrien02382
  • JohnNY
    Old thermostats used to have a little anticipator slider inside with a little arrow pointing to "longer". If you see that, slide it all the way toward the longer direction.
    Classes
    Canucker
  • ChrisJ
    How would that make a TRV work better?