EDR of straight pipe?
Dsisson
Dsisson Member Posts: 110
I have "The Lost Art of Steam Heating". I remember reading in it *somewhere* that one can use uninsulated pipe as a sort of a radiator for small spaces. I also seem to recall that it had a table that listed the EDR of different pipe sizes per foot. But for the life of me I can't find it in the book and I even wonder if I was imagining it. Can anyone point me in the right direction for a table that lists the per foot EDR for black pipe?
    Jamie Hall Member Posts: 27,046
    Why bother with a table? A few seconds with your tape measure and a friendly calculator will give it to you. Measure the circumference of the pipe in inches. Multiply that by 12 (the number of inches in a foot) and divide by 144 (square inches per square foot) and there you are. The EDR of a foot of your pipe.
  • Dsisson
    edited October 2020
    Thank you - as I understand it:
    EDR of steel sched. 40 pipe (example)
    pipe size = 1"
    diameter = 1.315"
    EDR per foot = 0.344
    correct?
    EBEBRATT-Ed Member Posts: 19,938
    yes. 3,14 (pie) x 1.315 (diameter) = 4.129 x 12"=49.5492
    49.5492/144=.344
  • ted_p
    ted_p Member Posts: 67
    edited October 2020
    Here's one:
    And Here's the link:
    Carbon Steel, ANSI Schedule 40 (in) Datasheet
    Use the numbers in the "External Surface Area" column.