HYdrolevel cycle guard
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
It’s coincidental timing that you write this, @clammy. I was about to also.
When my new boiler was on a pallet in my garage for about a year I was sure I was going to trash the cyclegard and replace it. But in the last 6 months, I slowly reversed my thinking.
one thing that affected me was: I was messing with my old boiler and got it into a state where the water ph was a little high, like 10. I was also draining it while it was firing, to test the LWCO while I was at it. The thing that concerned me was that the LWCO didn’t trip! I was watching the water drain out below the LWCO probe but it kept running.I flipped off the power switch and went “hmm”. I turned it back on and the LWCO tripped immediately. My theory is the heavy boiling, ph-heavy water was keeping the probe grounded.
it made me think about the cyclegard. It lets the water settle down to its actual level.
And now that I have the Peerless-supplied one in use to see it, it’s really nothing. It’s off for one minute. It’s more cycles, yes, but I’m convinced it’s WAY safer.Peerless must agree because the only reason they could possibly have for supplying it is fewer boiler failures.NJ Steam Homeowner.
Oh one more thing that is kinda weird! The Cyclegard performs its periodic checks even during the time when there’s no call for heat!! (At least the way Peerless wired it on my boiler)
@ethicalpaul, It's hard to determine anything about the old LWCO when the old probe or the unit itself could have been failing. Also, you knew the PH of the water was off and that can cause foaming which is know to cause the probe to falsely sense the water level is up above the probe. Turning the power off to the boiler probably gave the foam enough time to settle down and hence the boiler shutdown when you powered back up. In any case, I guess either the Safegard or the Cyclegard work as designed. It just seems counter intuitive to interrupt a boil to check the water level every 10 to 20 minutes.0
I think it’s intuitive. All those issues happen often enough in real people’s boilers in actual use. Stopping the boil for a minute gives a chance for a more accurate level check to occur
Not intuitive to me. If a boiler has enough water in it for the probe to remain wet, it doesn't need to stop every ten minutes to verify that the probe is wet. Having said that, I would agree that foaming or very turbulent water may fool the LWCO but one would think the reason for those issues should be identified and resolved and not depend on the LWCO to have to shut off every ten minutes. I do realize some HO's could care less about keeping their boilers running optimally and for those HO's the Cyclegard may offer a little more comfort. I'm good with whatever makes people happy with their systems. I love your install, BTW!ethicalpaul said:I think it’s intuitive. All those issues happen often enough in real people’s boilers in actual use. Stopping the boil for a minute gives a chance for a more accurate level check to occur
Several things.
Fred, if someone can care less, it means they do care some amount. The proper term is "couldn't care less" meaning they do not care at all.
Second, it's my job to make sure my water chemistry is correct, not the LWCO. It's also my job to make sure the equipment is in proper working order.
In my case, I will not be using a cyclegaurd.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Sounds like you shouldn’t need a LWCO at all @ChrisJ. What are ya, chicken?
PS thanks @Fred! You helped me on my very first post with my old boiler 😃NJ Steam Homeowner.
During the weeks, sometimes months my system runs without any water being added there is a chance it could run low. Especially during a cold week if I were to get sick etc and do not wander down there.ethicalpaul said:Sounds like you shouldn’t need a LWCO at all @ChrisJ. What are ya, chicken?
My water chemistry isn't going to mysteriously change without me doing something.
I do agree with @clammy to an extent though. On systems that are badly neglected the cycle guard could be beneficial. Foaming is bad, and would fool a probe LWCO.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Had a SGO gold wet based boiler installed last month with Riello 40 NG burner. Weil Mclain ships cycleguard as standard trim lwco now. I checked other manufacturers and it seems they all do ship the cycleguard on standard trim with steam boilers. The bottom line is there must be some data point (e.g. bad installs) that the cycleguard has managed to mitigate.
For a well installed system I think it sucks. I have the 15 minute one and yes it checks 15 minutes 24/7 whether boiler is firing or not. 60 second lockout, then 30 second burner purge = 13.5 minute max firing cycle at any given time. I will say this control is getting one helluva workout!
I don't really like it but the installer set best to use their standard lwco product in unlikely case ever a warranty issue. I mentioned swapping it out for a safeguard and he just shrugged, maybe later but will let it go for at least a season, dropped enough cash in last few months!
Yes, I suspect the data point is the volume discounts these manufacturers can get for the Cyclegard. One other point I might make, most gas valves are built and tested to provide about 100K clicks (give or take about 2%) With the Cyclegard, I would suggest you are also reducing the life of the gas valve by about 50%, maybe even more. Oddly enough, I have a 37 year old Burnham boiler. It is on its 3rd gas valve. The first two each lasted 17 years and I'm on the 3rd year of the 3rd gas valve. In theory, with the cyclegard, I'd be on gas valve # 6 or 7. Of course, if the boiler rots in 9 or 10 years, the gas valve may last the life of the boiler otherwise, Repair Parts sales is a big and profitable business as well.nde said:Had a SGO gold wet based boiler installed last month with Riello 40 NG burner. Weil Mclain ships cycleguard as standard trim lwco now. I checked other manufacturers and it seems they all do ship the cycleguard on standard trim with steam boilers. The bottom line is there must be some data point (e.g. bad installs) that the cycleguard has managed to mitigate.
I don't really like it but the installer set best to use their standard lwco product in unlikely case ever a warranty issue. I mentioned swapping it out for a safeguard and he just shrugged, maybe later but will let it go for at least a season, dropped enough cash in last few months!0
- 87.1K THE MAIN WALL
- 58 Biomass
- 117 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 55 Water Quality