One-pipe Riser Reroute Headache
lowballj
Member Posts: 15
Putting an addition on my house to expand the kitchen and connect to the family room. Riser to the bathroom radiator above the kitchen is in the way and needs to be rerouted.
Contractor in charge of the project said his plumber "is the best" "knows steam" "deals with it all the time" "can bang this out no problemo"
What I ended up with... 1/2" copper pipes, lots of elbows, and questionable pitch.
Already called up the steam experts near me to come re-do it.
I assume the previous pipe diameter was 2"... should I try to keep it the same?
If horizontal pipes are correctly pitched, are two 90 degree elbows near each other ok? I worry about condensate and steam collision, especially with smaller diameters.
Before and the current "after" pictures attached
@Danny Scully left you guys a voicemail0
Well... what was put in will never work... not that there aren't ways it could be done, and if you can get @Danny Scully on the job, he will fix it for you.Br. Jamie, osb
There are to many horizontal runs for a 1/2" pipe to work. To much condensation will run down that riser. The banging will be horrific and you will get no heat to the radiator.
What you may get away with is an 11/2" riser and a a 3/4" return piped to the wet return. Or pipe the return to the dry return using a water seal before tying into the dry return. Do not use a steam trap.
see attachment
Jake
Water seal taken from my book
Steam the perfect fluid for heating and some of the problems.
Steam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
I hope to see the "after after" pics!NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el0
Forgot to send you a guide to horizontal run outs based on the edr of a radiator. Based on what I see you have several horizontal run outs.
Hope that will be helpful for your project.
Jake
great job. No shortcuts or copper pipe,
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
If that pex is feeding a full bathroom group, wouldn't the code tables say it needs to be min 3/4" id?0
- 85.2K THE MAIN WALL
- 55 Biomass
- 72 Chimneys & Flues
- 129 Geothermal
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 878 Plumbing
- 5.9K Radiant Heating
- 375 Solar
- 14.6K Strictly Steam
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
