Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Can I run supply in the wall down to baseboard units?

Options
Jay_5133
Jay_5133 Member Posts: 1
I am currently remodeling an old farmhouse and will be installing baseboard units. In one area of the house I am unable to run supply and return lines from below. My question is can I run the supply and return lines in the wall down to the units? I'm concerned with air being trapped at the high point in the ceiling?

Comments

  • Ironman
    Ironman Member Posts: 7,376
    Options
    With proper purge valves and a manual vent at the high points, it should be fine.

    Also, keep the piping and pump sizing to maintain 3-4 FPS velocity.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Jay_5133
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,536
    Options
    And if they are in an outside wall make sure to keep them on the warm side of the insulation
    Jay_5133
  • Big Ed_4
    Big Ed_4 Member Posts: 2,785
    edited July 2020
    Options
    Water will freeze , attics and outside walls are avoided . Find a better way ...

    There was an error rendering this rich post.

    Jay_5133
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,536
    Options
    Too many unknowns. Inside wall or outside wall? Heated space above or attic above?