Plug valves for balancing heating system
Zman
Member Posts: 7,609
I am working on project where the steel threaded pipes and being eaten just after the valves where the threads are cut in. I am wondering about the suitability of plugs valves used for balancing. Does anyone have thoughts or experience with these valves as balancing valves? https://www.dezurik.com/resources/dezurik-eccentric-plug-valves-pec--pef-.5-3-pec-eccentric-plug-valves-bulletin-12_00_1a.pdf
Albert Einstein
Albert Einstein
Their info claims it is idea for balance. Ideally you would size by Cv not line size. That is important for balancing, valve authority.Bob "hot rod" Rohr
They may have originally balanced these based of delta t or an estimate based off percentage closed/open. The are no ports for hydronic manometer anywhere.hot_rod said:Their info claims it is idea for balance. Ideally you would size by Cv not line size. That is important for balancing, valve authority.
I am making recommendations for steps that need to be taken to solve the corrosion/erosion issue and really am just trying to figure out if the valves are part of the problem. Since most of them are seized, they definitely are not part of the solution."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
@Zman
I have seen hundreds of those and I hate to be blunt but they SUCK! I don't think I have ever found one that was not seized. Taco used to make a plug valve type (they dropped it) and they were popular around here but always froze up. Without tappings to check flow they are useless.1 -
If the goal is to check and be able to balance flow, invest in a quality balance valve. Quicksetters are nice if you want to make ongoing adjustments to dial in a system with unknown flow spec.Bob "hot rod" Rohr
That is going to be my recommendation. There will be lots of them.hot_rod said:If the goal is to check and be able to balance flow, invest in a quality balance valve. Quicksetters are nice if you want to make ongoing adjustments to dial in a system with unknown flow spec.
Albert Einstein0
- 120 Geothermal