Radiator steam traps
gh2538
gh2538 Member Posts: 4
Looking for more info about these traps as I was unable to find any data in the books. The boiler we installed 18 years ago rusted out prematurely and as I recall this boiler always cycled on room thermostat and never reached 1.5 psi cutout....go figure LOL
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,681
    Weighted check. The hole is for air and a bit of steam. The weight of the trapped condensate opens the check. The condensate level in the radiator drops. The weighted check cycles closed again.
    Retired and loving it.
  • JohnNY
    JohnNY Member Posts: 3,336
    I love that offset, eccentric bushing.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Steamhead Member Posts: 18,174
    Donnelly system, right? As shown in chapter 15 of Lost Art?
    All Steamed Up, Inc.
    Towson, MD, USA
    Oil & Gas Burner Service
    Consulting
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,917
    It looks like someone drilled and tapped the end cap. The rococo border gives it away.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
    No, that's actually an eccentric bushing. They actually did make bushings with fancy borders back then, both standard and eccentric. We might have a couple laying around at the shop.
    If we have to put something like that together now, we'll use a double-tapped oil tank bushing and plug the unused hole.
    Towson, MD, USA
    Consulting
    Hap_Hazzard
  • Hap_Hazzard
    Wow. I don't know what's more amazing: that they made bushings like that or that the installer would take the trouble to use a bushing that matched the style of the radiator.