HTP Fire Tube Boiler overheating
Redicliff
Member Posts: 1
in Gas Heating
We have an HTP flash heater MC-100 that is overheating.
I've posted a 1.5 min video of the control panel as the unit cycles.
https://www.dropbox.com/s/cuakr4pa010f2xq/HTP Boiler Overheating.mov?dl=0
Not finding corresponding troubleshooting recommendations in the manual. Of course, if it's there, it probably reads "call a certified tech". But, we're sheltered in place a long ways from a tech.
Comments and recommendations appreciated
Or no or low water pressure in the system.0
Check your pumps..water isnot moving thru HX..0
Not enough flow, can hear it boiling in the HX. How's it piped?0
they can be tricky to purge the boiler on fire tube design. i have had to hold the relief valve open if you do not have enough purge flow or pressure.Bob "hot rod" Rohr
Whats the boiler pressure? Should be a guage under the boiler?
Upload more pictures, sometimes we can see issues..0 -
If this in fact an MC series boiler , it is not a firetube . MC Series was a water tube boilerYou didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38331 -
How old is boiler?
Could HX be plugged?0