HTP Fire Tube Boiler overheating
Redicliff
Redicliff Member Posts: 1
We have an HTP flash heater MC-100 that is overheating.
I've posted a 1.5 min video of the control panel as the unit cycles.
https://www.dropbox.com/s/cuakr4pa010f2xq/HTP Boiler Overheating.mov?dl=0
Not finding corresponding troubleshooting recommendations in the manual. Of course, if it's there, it probably reads "call a certified tech". But, we're sheltered in place a long ways from a tech.
Comments and recommendations appreciated
  • kcopp
    kcopp Member Posts: 4,700
    From the description you are not getting flow. Is something shut off, circulator broken or debris plugging the piping?
    ZmanGroundUpBillyO
    EBEBRATT-Ed Member Posts: 20,485
    Or no or low water pressure in the system.
  • fenkel
    fenkel Member Posts: 162
    Check your pumps..water isnot moving thru HX..
  • GroundUp
    GroundUp Member Posts: 2,527
    Not enough flow, can hear it boiling in the HX. How's it piped?
    hot_rod Member Posts: 27,857
    they can be tricky to purge the boiler on fire tube design. i have had to hold the relief valve open if you do not have enough purge flow or pressure.
  • fenkel
    Whats the boiler pressure? Should be a guage under the boiler?
    Upload more pictures, sometimes we can see issues..
  • Rich_49
    Rich_49 Member Posts: 2,783
    If this in fact an MC series boiler , it is not a firetube . MC Series was a water tube boiler
    You didn't get what you didn't pay for and it will never be what you thought it would .
    732-751-1560
    Rich McGrath 732-581-3833
    kcopp
  • fenkel
    How old is boiler?
    Could HX be plugged?