Stat with 12k sensor
It is a curve that varies by specific thermistor. Simply knowing the 25 c resistance doesn't tell you enough about what its curve is, there is another parameter or 2 that indirectly describes the slope of the curve.0
I should have explained better..... I have an existing stat that uses a 12k ohm floor sensor. The idiots that installed it didn't make it accessible for me to be able to change it. I need to change the thermostat so if I want to continue to use the existing floor sensor I need to find a stat that uses 12k instead of 10k.0
And what, we're going to assume the return is going to be the temperature of the floor? I don't think I want to go there. I know the Europeans use 12k sensors so I really just want to find a Stat available here that uses it too.
Thank you though.0 -
Shop some offshore suppliers, Amazon UK for example
Salus is a common brand in EuropeBob "hot rod" Rohr
Actually the return should be a few degrees above the return.Jeff Perry_3 said:And what, we're going to assume the return is going to be the temperature of the floor? I don't think I want to go there. I know the Europeans use 12k sensors so I really just want to find a Stat available here that uses it too.
Thank you though.
Sorry
A few degrees above the floor temp.0 -
It may be possible to use resistors to tweak the 12K sensor into something close enough to 10K to use. It probably wouldn't be terribly accurate across it's entire range, but it should be good enough at the target temp & some few degrees on either side.0
Maybe if you calibrate it for a specific temp. It wouldn't work well if you changed the setpoint by more than a couple degrees from the point you calibrated it at.ratio said:It may be possible to use resistors to tweak the 12K sensor into something close enough to 10K to use. It probably wouldn't be terribly accurate across it's entire range, but it should be good enough at the target temp & some few degrees on either side.
Right. Not perfect by any means, but if you dial it in at the temp you plan on running at, you should be fine. At worst, you'd have to think of the settings as 'warmer' and 'cooler', rather than a whatever° temp setpoint.mattmia2 said:Maybe if you calibrate it for a specific temp. It wouldn't work well if you changed the setpoint by more than a couple degrees from the point you calibrated it at.
The first 12K thermistor table I found (PDF here) shows around ±1 KΩ difference for 2° C around 25° C (77° F), which is a fairly close match for a 10K type 2 sensor, with types 3 and 4 being progressively poorer matches.
- 109 Chimneys & Flues
- 975 Plumbing
- 386 Solar
- 17 Recall Announcements