Smith Boilers

EBEBRATT-Ed
EBEBRATT-Ed Member Posts: 15,455
I was on the Mestek web site and couldn't find Smith boilers. I know Peerless was making the same boiler is Smith completely gone?

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,506
    edited February 2020
    Looks like it re-directs you:
    http://www.smithboiler.com/
    Says for more info on Smith Boilers...
    http://mestek.com/hvac-metal-forming-articles.asp?type=1&lang=en&id=60#.Xkla4TJKiHs
    What are you looking for in particular?
    steve
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    @STEVEusaPA

    Well Smith is owned by Mestek that owns a bunch of other companies. I used to go to the Mestek web site and scroll through to find Smith.

    When I went on this morning (haden't been on it in a while)
    I hit "companies owned" and Smith isn't listed.

    So being that Peerless is now making the Smith #19 & #28 & maybe others under their own label (they have been using the same foundry for quite a while now) I thought Smiht may have closed up, guess not.
  • B_Sloane
    B_Sloane Member Posts: 56
    19's and 28's have been very good for me !
    used to spend all summer replacing sections and gaskets :)
    Precaud
  • Steamhead
    Steamhead Member Posts: 16,796
    B_Sloane said:

    19's and 28's have been very good for me !
    used to spend all summer replacing sections and gaskets :)

    Welded headers?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    28s came out in 1977 and I don't recall anyone having problems with them back then, they seamed bullet proof all through the 80s and 90s but something has changed along the way. Now they seem to fail like all the others.

    Now they use a perforated dip tube on the water boilers to distribute return water among the sections instead of dumping it in the back.

    I have only done a few of the 19s
  • B_Sloane
    B_Sloane Member Posts: 56
    Steamhead said:

    B_Sloane said:

    19's and 28's have been very good for me !
    used to spend all summer replacing sections and gaskets :)

    Welded headers?
    in many cases, yes..
    but not the cause of failure
    most were casting defects in intermediate sections
  • B_Sloane
    B_Sloane Member Posts: 56
    I once bought 16 #28 Sections for the same boiler room
    multiple 17 Section Model 28's :)
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,215
    Funny thing is Smith permits welded headers on the 28, while Peerless, with the same casting for the TCII does not permit welded headers. It's probably because Smith is under the ECR unbrella... lower standards from my experience.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    @The Steam Whisperer

    Problem with welded headers is when they come out of the boiler with a 90 and go into the header close coupled.

    If you come out of the boiler and go horizontal for some distance it's not as bad, even 5" will give a little

    Bad as it is most will not struggle with the 5" fittings you need on a 28.

    I'll bet 99% of the smith, weil and burnhams are piped with welded headers. The stuff made now will rot before they crack at the top :)
  • ScottSecor
    ScottSecor Member Posts: 851
    We see welded headers often with commercial cast iron sectional and almost always with scotch marine type boilers. I have never personally witnesses a boiler failure related to welded headers. Not saying it doesn't happen, but the premature commercial steam boiler failures we see are almost always related to poor water condition or lwco failure.
  • retiredguy
    retiredguy Member Posts: 898
    The company I worked for corrected cracked sections on the H.B.Smith series 28 boiler sections, caused by cold water shock by installing a "run around" pump piped from the discharge to the return tapping. This solved almost all the cracked sections on a hot water heating job. When using the boilers for steam we had very few section replacements. In the 1960's through the early 2000's most of the boilers we sold and supplied for commercial buildings (schools and buildings) were the 3500's, 4500's, and the 6500's. fire box refractory lined design. These boilers had almost a zero failure rate unless the heating engineer did a very poor job in the heating system design. Then they brought out the "wet base" 28 series boilers. They were supposed to be more efficient, and maybe they were but they really kept us busy replacing sections, until the run around pumps were installed.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    @retiredguy

    Your right. When I started (73) almost every job in my area was a Smith boiler. Of course the fact they used to be made 10 miles from here was a factor they had this area tide up solid.

    3500, 4500, 6500s were good boilers if you could keep the insulating cement between the sections. With the built in headers they were good steamers for the most part but we always thought of them as high maintenance boilers. But you cold replace a section without taking the whole thing apart or plug off a section to keep it running.

    But Weil McLain had the 86/88 so Smith had to come out with something to compete.

    Blend pumps do help I know Burnham requires under some conditions
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,215
    Yes, I am aware of the problem that welded headers cause, that's why we use drop headers with threaded fittings. 5 inch threaded isn't that bad to work with. 6 inch is a big step it seems. It mainly comes down to upfront cost. A 5 inch welded fitting is about 1/5 the cost of a threaded fitting, so welded is what gets used. I have found the WM LGB's seem to be the most susceptible to the levering of welded headers... The typical life we see is about 14 years. In contrast, a single riser LGB will often will last 24 years. We see leaking sections gaskets regularly on these. The Peerless 211A seem to hold up pretty well as do the WM88 when installed all welded. However, I bet both would last a lot longer with threaded fittings.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    @The Steam Whisperer

    I was running 2" copper on a job years ago and was worried about expansion (hot water system) was about 250' long. So I decided to pipe in an expansion loops every 50 feet. I think in 250' the expansion was around 2"

    So I made some expansion loops out of 2" copper with 4 elbows. Actually, Carrier had a piping book that describes how to size them. It's the only book I have seen that describes it specifically.

    After I assembled these they were about 3' and 3' over I put one on the floor and put some pressure on it. It would move 1/2" easily with minor hand pressure

    Even 5" if you give it some room will flex a little.

    I don't like the way drop headers look but in this instance they do a lot for stress relief on a boiler even if they are welded
    B_Sloane
  • ethicalpaul
    ethicalpaul Member Posts: 5,695
    > I don't like the way drop headers look

    Heresy!! 😂
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
    Hap_HazzardPrecaud