Mechanical Room Repipe

EzzyT
EzzyT Member Posts: 1,294
We were called in to take a look at the endless issues plaguing this boiler issues with the system.
Found that the near boiler piping was all wrong as you will see in the pictures. The boiler would short cycle like mad and whenever the boiler would go for trial for ignition there would be a very boom which was clearly due to improper flue and air intake pipe size.
We added a buffer tank to stop the boiler from short cycling and power flushed out all debris that was in the system.
E-Travis Mechanical LLC
Etravismechanical@gmail.com
201-887-8856
DZoro

Comments

  • hot_rod
    hot_rod Member Posts: 22,024
    nice work in a tight space.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EzzyT
    EzzyT Member Posts: 1,294
    @hot_rod thanks.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    Nice job!!

    Hard to make it look nice in a tight space, but you did that
  • Beautiful. That looks like a one-man job since there's no room for anyone else.

    The Grundfos supply pump to the indirect is installed with the shaft in the vertical position. You might want to change that on your next trip.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    Intplm.
  • Intplm.
    Intplm. Member Posts: 1,883
    I've never said this before , but that is ten pounds of beautiful in a five pound bag.
    Looks great. Nice job.
  • EzzyT
    EzzyT Member Posts: 1,294
    Thanks gentlemen. @Alan (California Radiant) Forbes the Grundfos pumps are the old pumps.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Ironman
    Ironman Member Posts: 7,367
    Great job. We've used a few of those HTP buffer tanks. very reasonably priced for a SS buffer tank.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • BillyO
    BillyO Member Posts: 277
    Nice job, too bad you used an HTP on wall
  • clammy
    clammy Member Posts: 3,103
    As always Ezzy ,you found the issues and straighten it all out and now it s running and working properly like the first contractor could not do . Kudos to you and Fred as always great work executed properly and completed something a lot of contractors cannot do when u send out boys to do real mechanics work . I really think it all starts out by reading the instruction and understanding what u read and having a bit more knowledge then is required to fog a mirror which is usually the only requirement to work at some places . Great work ezzy but I always know what to expect from you guys a job well done . Peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating