It comes this way!
EdTheHeaterMan Member Posts: 11,643
Don't oil burners come out of the box already properly adjusted?
Before you criticize the installer, Look at the top left portion of the furnace!
    Steamhead Member Posts: 18,252
    I'm not a scorched-air guy by any means- but I'd have to be very drunk to think that was OK. The same might be true of the inspector.
    In both cases- You can't fix stupid!
    And I'll bet that approval sticker will make it difficult for you to sell and install the correct model................
    Consulting
    EdTheHeaterManIronman
    I told the owner that I won't fix the oil leak I was originally called to fix unless the burner is made right. I sent the landlord a picture of the page in the instructions manual and before and after pics of the burner. Cost him at least 1/3 of the price of there original install.
    It's right now!
    Yours truly
    Ed
    How about posting the "after" pic here? I know we all know what you did, but there are those out there who will need to actually see it.....
    Consulting
    kcopp
    mattmia2 Member Posts: 15,767
    side draft?
    HVACNUT Member Posts: 7,267
    That was shipped for horizontal installation but I guess the installer thought otherwise. Silly Rabbit.
  • BDR529
    BDR529 Member Posts: 372
    I get dizzy looking at it!
  • STEVEusaPA
    edited December 2019
    I don't see a hole for a combustion test lol.
    And you know that pump strainer is never getting changed
    This is why I was Called:
    This is what I Found:
    This is how I left it
    Not a fan of the refrigerant line going in front of the oil burner, but the customer has a budget. :/
    The leak was in the compression fitting at the oil filter outside. New fuel line, and rotate the burner properly.
    There is a hole in the vent connector. It is on the other side where it is hard to see
    STRAINER? Who needs a stinkin' strainer? Don't we throw them away after they clog?
  • jumper
    jumper Member Posts: 2,502
    Well horizontal furnaces can be installed vertically for "upside down" applications?
  • Intplm.
    Intplm. Member Posts: 2,856
    @EdTheHeaterMan No?! No....is that a approval inspection notice from a inspector?
    The pics a bit blurry. Holy S**T !
  • rick in Alaska
    rick in Alaska Member Posts: 1,517
    Off topic for this post, but I see this quite often on this site. Is your fuel that bad where you are, or is it because your tanks re buried and just old.
    I do not know of anyone who has changed a pump screen here, and I have personally only ever changed about a dozen pumps in 27 years. We just don't see sludge here very often. If it is, it is in a fuel tank in one of the low budget mobile home parks where the people sometimes are only putting in about 50 gallons at a time, and letting too much water accumulate.
    So I guess my question is this; Are you guys just dealing with old fuel tanks that are just sludged up, or is it bad fuel to start with?
    Rick
    There are a lot of really old tanks. starting with the refineries to the bulk plants to the homeowner tanks and the summer heat can cause more condensation inside the tanks. especially when the tanks are left below 1/4 of a tank for 5 months in a row.
    rick in Alaska
  • Ironman
    Ironman Member Posts: 7,879
    Is that cardboard between the furnace and the coil cabinet? If so, that inspector needs to be fired.
    Bob Boan
    neilc
    That's what happens when cost alone is the deciding factor.
    @Ironman I never looked at your observation about Cardboard. It is metal. I believe the contractor used the old Singer or York combustible floor base. That tan color is definitely metal