External Limit Open
Uncle_Cranky
Member Posts: 6
I had Joe Star* install a boiler (Triangle Tube Prestige Solo-110) a few years back and now I can't seem to reach him and I'm stuck. System was mostly without issue until last year when we had it serviced (by other). After the service, we got this same error message maybe once per month. It disappeared for the warm weather so it's somehow related to heating. Now that its heating season, its back and its daily or multiple times a day.
Had someone come look at it and he wants to replace the ignitor and flame sensor for $. I can't see why that would be the issue being that it fires up easily after hitting the reset? Unsure what the "external trigger" may be or if its something I can address myself.
Anyone recommend someone versed in Triange Tube boilers in the central jersey area? Thanks!
Dave
follow the other end and make sure it is secure. undo the terminal and make sure someone didn't clamp the screws on the insulation instead of the wire. pull the other end and make sure something isn't screwed up with the terminals on that end.0
Looks like you have wires on terminals 9 & 10. That is for a manual reset limit so you must have something there thats auto reset. Trace the red and white wire from thoses terminals and at the end of them should be your trouble.0
check "find a contractor" on this site0
Uh... yeah... kind of. There are two possibilities: the low water cutoff is malfunctioning, or you are low on water. Neither one is to be trifled with, and you should turn the boiler off until you have a chance to fix the problem.Uncle_Cranky said:Low water cutoff? Sounds important.
While 11 and 12 were very tight, I was able to get a 1/4 turn on both 9 and 10. I’ve never personally seen a red light on the low water cutoff.
Does the fact that this only happens with the heat on (hot water baseboard) mean anything?
Your boiler has a pressure actuated low water cut off from the factory. Any idea what size pipe that the control is in. I can't tell if thats somekind of home made fitting and maybe the probe is touching the inside of the pipe. What is the boiler pressure reading at the little round gauge on front of boiler. Also it looks like the valve next to the side of the boiler is about 3/4 shut, why?
If the pressure is above 12# and the house heats ok when it runs it is most likley a bad control. Don't call the people who want to change the igniter too do it. You can do with out that control since the boiler has it's own LWCO safty but it wouldn't hurt to have some one give it the once over. TT phone # is 856-228 8881 see if they can recommend someone in your area that has factory training.1 -
If any of this has helped you please see this thread its either 1 or 2 on the wall.
Please help the Franciscan Sisters of Kansas City0 -
Thank you.
Thanks buddy.0
After 3 days without issue, I woke up to a cold house this morning. Called Triangle Tube, who is ironically 1.5 hours away from my house and they don't have a local recommendation? Anyway, they referred me to their distributor who referred me to someone. Thanks everyone for your help!0