Expansion tank that can handle more heat
CBRob
CBRob Member Posts: 291
A home that I manage has a poorly placed expansion tank, it's on the cold side of the tank but close to a recirc pump that keeps it too hot.
I'll probably try to put a little heat trap loop before the tank but I'd like to know if there are dhw tanks that can handle more heat
  • JUGHNE
    JUGHNE Member Posts: 11,549
    How do you know it is getting too hot?
    Most true DHW exp tanks are rated for pretty high temps.
  • Zman
    Zman Member Posts: 7,609
    DHW expansion tanks can handle more heat than the occupants or the relief valve. What are the symptoms?
    Albert Einstein
  • CBRob
    edited November 2019
    Just replaced it last year and it is full of water already.
    I'll take a pic tomorrow of how it is situated
    I'm guessing the failure is heat related...
    Could be something else.
  • STEVEusaPA
    What’s your incoming water pressure?
  • CBRob
    I have not put a gauge to it, but there is a regulator with a 65psi high end.
  • JohnNY
    JohnNY Member Posts: 3,365
    DHW expansion tanks are typically factory pre-charged to 40 PSI. Isolate and pump up your tank's air pressure. Problem solved.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    CBRob
  • DZoro
    DZoro Member Posts: 1,048
    What model of tank are you using? Is this on the domestic water? Boiler water? There are differences between DHW tanks and Radiant heating tanks.
    D
    CBRob
  • CBRob
    John was right, I just needed to pump it up.
    It's at 50 psi now and holding air.
  • CBRob
    DZ,
    I found the tank on the radiant heat was incorrect... same house.
    Swapped in a rx30 .
    Also noticed the circ pump installed with a vertical shaft, but I think that is ok with adequate psi in the system. I saw another discussion here at heating help that talks about pumps installed incorrectly
  • CBRob
    Can I use the flex2 dhw tank that I removed in another dhw application?
    It's not fubar from being exposed to glycol?
    Jamie Hall Member Posts: 27,369
    No. Once it has been exposed to glycol, you mustn't use it for domestic (drinking) water.
    CBRob