Taco Zone Valve hack?
Thanks,
Hasty-order-button-clicker
Nope. Can't you return them, or did you already install them?
@heritageproperties
Sounds like you got your hands on the Zone Sentry.
You don't have to replace the entire zone valve especially if the valve body is installed. You can get a new powerhead to change from normally open to normally closed.
Dave H.Dave Holdorf
Taco, Inc
3 -
If I got this right the valve is open when there is no power to it and it closes when you power it. If thats how it works you can use a 90-340 relay and the power the valve through the NC contacts and tie the tstat to the relay coil and that will open the contacts and drop power to the valve.0
RIB relays for around 10 bucks is an inexpensive way to do this.
We use them when you have a valve that needs power to open and power to close.
One issue with N.C valves is they end up powered for a lot of the year, probably shortens their life.
Living the hydronic dream2 -
Do yourself a favor... get the correct valve. if the manufacturer of that valve has a NC valve you may get off easy by just changing the guts without soldering the new valve body.
Put the wrong guts on the unused valve body and sell them on eBay or Craig's list.Edward Young Retired
Can you reverse the wiring on the internal 24v motor?
that would require people to read the instructions.
I think it's a fair question and an opportunity to teach
With DC wiring, it may be just that easy. With the 24 VAC control current normally used in HVAC controls, that may not be the case. That's because the current travels in both directions at 60 cycles per second, so reversing the wires will cause the current flow in both directions at 60 cycles per second. No difference.
Another problem may be in the design of the actual valve. If the valve has a spring to open and needs power to close, then reversing the wires on a motor will not change the fact that the spring will always open the valve when there is no power. The OP would need to change the design so the spring would close the valve and then power the valve to open it by reversing the motor direction. Not so easy if you don't own a machine shop with all kinds of drills and lathes and a stock of different springs so you might find just the right one for that valve.
But that was a fair question for @jacoblahr. Welcome to the forum. Be sure to read the rules by clicking at the top of the page or
Hereare the website rules, as well as some tips for using this forum.Edward Young Retired
The OP asked about spring loaded valves.
Power open closed are a different animal.
If you're asking if it matters which motor lead connects to 24 volts or Common, then no. The motor doesn't care.
OP mention Taco zone valves, does Taco sell a spring return ZV? I see the 555 thermal, and the capacitor discharge zone sentry?
So the only Taco ZV with n.o. , n.c. Option would be the zone sentryBob "hot rod" Rohr
I guess Taco does sell a motorized spring return valve. Looks a lot like some other brands😗
I don’t see a n.o. Version offered?
Flair zone valves were also power open, power closed. Hateful things.
Generally big fan of random hacks, so took a quick look at a Taco valve.
@jacoblahr is correct. The internal motor is DC and you can reverse the wires on it. There is no physical end of travel switch, look like the motor runs until a current limit is reached which is considered end of travel.
The one issue with this type of hack is eventually somebody else will have to fix this. They will not know about what is inside the valve and replace it like for like creating a lot of headache. At minimum I would do a future a solid an include a tag on there about the mods.
I've been slowly de-hacking my house heat specifically to avoid the above issue. These are hard enough to troubleshoot, adding extra complication is cost more than getting the right part.
- 123 Chimneys & Flues