Water Hammer in steam pipe above boiler shuts boiler off when steam begins to go up in steam pipe
jovo37
Member Posts: 10
Hello, thank you in advance for taking time out and looking at my issue. I have a 1 year old Weil Mcclein steam boiler. I recently just started hearing a water hammer in the steam pipe above the boiler when the steam starts to go up into the pipes for the radiators. The hammer just started after a month of use. It will bang for a few seconds, and when it does the Boiler will shut off, when this happens I shut heat off and put it back on using the thermostat and it resumes and seems to run fine after that. What could my issues be? Thank you.
You'll get quick answers if you supply good pictures of the piping above and around your boiler. Mo' pictures and information = mo' bettah answers.0
Photos of near boiler piping0
My opinion is that due to incorrect boiler piping (it’s quite incorrect) the boiler is throwing a lot of water into your main and triggering a low water condition stopping the firing cycle.NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el4
Is it difficult to repipe it correctly for a competent plumber0
Where are you located @jovo37?0
Brooklyn ny @Danny Scully0
It is piped so wrong but hammer occurs when water is pooled somewhere, typically in the area where the hammer originates. If this is a one year old boiler, I'd have someone with real steam knowledge come in and pipe it correctly. Get your Owner/Installation manual out and look at the manufacture's recommended minimum piping configuration.
Has the boiler ever been skimmed? What is the Pressuretrol set at?0 -
Pressuretrol set at 1.5, it’s been skimmed in the past0
Certainly can be done. Not a small job. Is there anywaythat you can get the original installer back and have him repipe correctly? The current piping is an abomination.1 -
Water thrown up into piping....auto feeder comes on and shoots cold water into the top of hot boiler....could it flash to steam raising the pressure and shutting down by pressure control??
Just a theory.....
Or water leaves and LWCO shuts boiler down, auto feeder might come on....but eventually the boiler would be over filled/flooded.
Then pressure control would shut down quickly.
The entire install reminds me of the Larry, Moe and Joe plumbing show.
Could we get a picture of the side of the boiler where the gas pipe is. The returns must be all there.0 -
At a glance it should be hard to convert to a drop header. It should go up off the boiler elbow hard 180 defeats to plot down then right angle towards the two mains. Connect those with tees then 90 over to the equalizer
Most plumbers won’t touch boilers and just have no experience. But yes they can do the pipe fitting work.
Knowing HOW and knowing WHAT to do are completely different things.0 -
Competent Plumber after calling electrician friend came needed another skimming and changed angle a pipe on the return.0
Did Competent Plumber have anything to say about your near-boiler piping?jovo37 said:Competent Plumber after calling electrician friend came needed another skimming and changed angle a pipe on the return.
NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241
- 85.7K THE MAIN WALL
- 49 Biomass
- 72 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 48 Industry Classes
- 15 Recall Announcements
