Tankless aquastat
Options

keith123
Member Posts: 105
If repurposing a tankless coil on a steam boiler for space heating, which a Honeywell aquastat would you use
0
Comments
-
-
-
Separate heating zone is correct0
-
L6006 or L4006 in the aquastat tapping on the coil. Set at 180 or lower. This will keep the boiler from steaming on a call from the hydronic coil zone.
set up the circulator relay as indicated in the diagram
1 and 2 are L1 and L2 or common
T T is from the zone thermostat
jump 1 to 3
power circulator with 4 (power) and 2 (L2 or common)
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Thank you sooo much !!0