To get hot water boiler only runs for a minute used to run for at least 3 minutes
bobbyromano
bobbyromano Member Posts: 8
edited October 2019 in Oil Heating
Had a tune up 3 weeks ago from a neighbors oil company who did it on the side. he screwed up because the boiler ran rough after he did it and i even told him it was running rough and his words were " I used the same nozzle that was on it". I ended up getting someone qualified who now has it running smooth but now when i use hot water the boiler only runs for about a minute when it would always run for at least 3 - 5 mins. Something is off as the boiler runs even when im NOT using the hot water for about a minute it will run and when i do use hot water the boiler will come on more often than usual to make hot water where in the past it would run a few mins stop and i was able to get a good amount of hot water and now the boiler has to run more frequently. Any ideas before I call this guy back?
Thanks
    Jamie Hall Member Posts: 26,174
    One thing you don't mention. Is the water, in fact, hot? That is, do you get hot water?
    From your description I would be looking at a control problem -- aquastat, perhaps -- rather than a burner problem.
  • bobbyromano
    Yes the water does get hot.
    Probably the aquastat then -- misadjusted, bouncing off high limit, or just plain not working right.
  • bobbyromano
    Ok. thank you. Will have someone look at it.
    HVACNUT Member Posts: 6,860
    You can look at it and post back. There should be a box with a grey cover on the boiler. Inside are temperature dials. Hi and Lo. What are the settings? And differential if there is one.
  • bobbyromano
    edited October 2019
    this is all i see thats a gray box
    That's the pressuretrol which controls the steam pressure. There should be another one somewhere... is your hot water generated by a coil within the boiler, or is it an indirect tank?
  • bobbyromano
    its on 160 but i dont think anyone touched that
    Found it. They may not have touched it -- but that doesn't mean it's working properly. Have it checked.
    bobbyromano
    Inside the aquastat cover is a white wheel with numbers. If it's at say, 5, then the burner runs until 160°, then when the temperature drops to 155° (5° differential) the burner starts again. Is it possible the differential was at 10 or 15 before the service was done?
  • bobbyromano
    I was pretty much there with people I had look at it so as far as I know no one touched that. I think because i was getting a ton of soot because someone screwed up the boiler was getting very hot. You think if the boiler got too hot it couldve screwed up the aquastat? If i take the cover off do i shut the power to the boiler?
    Yeah, shut off the boiler first.
  • bobbyromano
    This is all I see
  • bobbyromano
    looks like that dial is on 5
