To get hot water boiler only runs for a minute used to run for at least 3 minutes
bobbyromano
Member Posts: 8
Had a tune up 3 weeks ago from a neighbors oil company who did it on the side. he screwed up because the boiler ran rough after he did it and i even told him it was running rough and his words were " I used the same nozzle that was on it". I ended up getting someone qualified who now has it running smooth but now when i use hot water the boiler only runs for about a minute when it would always run for at least 3 - 5 mins. Something is off as the boiler runs even when im NOT using the hot water for about a minute it will run and when i do use hot water the boiler will come on more often than usual to make hot water where in the past it would run a few mins stop and i was able to get a good amount of hot water and now the boiler has to run more frequently. Any ideas before I call this guy back?
Thanks
Thanks
0
Comments
-
One thing you don't mention. Is the water, in fact, hot? That is, do you get hot water?
From your description I would be looking at a control problem -- aquastat, perhaps -- rather than a burner problem.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Yes the water does get hot.0
-
Probably the aquastat then -- misadjusted, bouncing off high limit, or just plain not working right.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Ok. thank you. Will have someone look at it.0
-
You can look at it and post back. There should be a box with a grey cover on the boiler. Inside are temperature dials. Hi and Lo. What are the settings? And differential if there is one.0
-
this is all i see thats a gray box0 -
That's the pressuretrol which controls the steam pressure. There should be another one somewhere... is your hot water generated by a coil within the boiler, or is it an indirect tank?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
its on 160 but i dont think anyone touched that
0 -
-
Inside the aquastat cover is a white wheel with numbers. If it's at say, 5, then the burner runs until 160°, then when the temperature drops to 155° (5° differential) the burner starts again. Is it possible the differential was at 10 or 15 before the service was done?0
-
I was pretty much there with people I had look at it so as far as I know no one touched that. I think because i was getting a ton of soot because someone screwed up the boiler was getting very hot. You think if the boiler got too hot it couldve screwed up the aquastat? If i take the cover off do i shut the power to the boiler?0
-
Yeah, shut off the boiler first.0
-
This is all I see
0 -
looks like that dial is on 5
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements