Btu's in hand, how to size radiator?
mikemac52
Member Posts: 58
I have my coolcalc manual J in hand and the Btu requirements per room. How close to come to the btu numbers required with the capacity of the radiators? Should I leave any headroom? The cast iron radiators were quite large and will be downsizing some of them for space saving reasons. (I mean, the wife told me to...)
Size them to the heat loss of the room within 5%.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
And, since this is tagged under hydronic, not steam, be sure to account for the temperature you plan for your circulating water.Br. Jamie, osb
If you are only downsizing some of the cast iron radiators, be careful of your zoning. If you have existing radiators which are 200% of design with new that are 105% of design, you would be wise to zone them separately or add TRV's"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Thanks for the quick replys! Hoping to keep the water at 140 F. Would have been 130 F but for a bad interior design Choice...0