Dunham system fast venting questions
Options
mstrbill
Member Posts: 37
I question how that little vent atop the dunham return trap can vent the whole house fast ? The system has a peerless oil steamer , large 5 bedroom home , original dunham componants , vapor- stat set correctly . Should i change the vent to a couple of gorton -2 s and will this help the entire system vent and then steam up quick ? Can you vent a vapor system too quick ? I always welcome your suggestions steamers !
0
Comments
-
No, you really can't vent a vapour system too fast -- but vents aren't cheap, so there's no point in going overboard. In your case, though, it may be that a bigger vent may help. Or vents. Try a Gorton #2 there and see what happens. While you are at it, check all the traps -- particularly the crossovers -- to make sure they are really working properly.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If the system is set up for naturally induced vacuum, you really don't need much venting since once the air is pushed out, just a little bit comes back in through leaks. I'd set it up with a check valve and a Big Mouth if it doesn't already have a check valve in the vent.To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
Right. A very small vent gets it done then. You want quiet, fast and efficient response .... just get the air out once and keep it out.The Steam Whisperer said:If the system is set up for naturally induced vacuum, you really don't need much venting since once the air is pushed out, just a little bit comes back in through leaks. I'd set it up with a check valve and a Big Mouth if it doesn't already have a check valve in the vent.
1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 418 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements