Gas Furnace cycles when thermostat is off
Szolusha
Member Posts: 5
in Gas Heating
Hi all hope I posted to right area, I have a 19 yr old Nordyne furnace, it is located in attic and is very well ventilated
if anyone saw it they would say its brand new. Any way I had a problem with it 2 yrs ago and it was the main circuit board had a crack in it, I replaced it and all worked fine. Note its only heating 2 bedrooms and a family rm , with the ac unit outside. Now I am having a problem where the unit cycles by itself meaning thermostat is in off position, we are not running the ac unit or heat , thermo is OFF and about 3 hrs later there's air being blown through the vents? then it shuts off and wont do it again for 2 maybe 3 days and the air will start again then stop? I am confused and wondering what I should replace or ck
any help would be great
Thanks Mike
Thanks Mike
Would you have a thermostat that has a "recirculate" feature on the fan selection? Or just "fan on" and "auto" selections.0
new thermostat with auto and off and its in the autoposition0
When this happens is it running the heat or AC with the fan?0
no nothing just air0
Did it start to do this when the new thermostat was installed?Br. Jamie, osb
nope replaced it 2 wks ago, it started about april this year , when the ac was on during summer , in the middle of nite when ac would shut off 2 -3 am then I would hear the blower kick on with air, then 10 -30 min later the ac kicked back on so its not something I can pinpoint exactly when it happens. So we would shut off the over ride switch to the unit, then last wk I went up cleaned unit and threw the switch back on and it went 3 days with nothing then at 4 in afternoon it was blowing air all with the thermo off.
Check the rollout & limit switches for rusty/corroded connections. Some controls will call for the blower if they think that the HX is hot even if they're not calling for heat.0
does it have a temp. sensing fan limit switch. may be getting hot enough in attic to cycle fan0
Ratio and uncle john that is exactly what I thought it mite be so I went ahead and ordered one when I replace I will update thanks a lot guys for all help , you too Jughne appreciate all avenues
Mike0 -
You stated you replaced the circuit board, so we're assuming (pic of the wiring diagram would be Gr8) the operating fan controls are relays and not a fan/limit (insertion)control. And the issue started even before you replaced the thermostat.
Like @JUGHNE wrote, it might be a short. I would just remove the wire from the G terminal on the board, and wait, and wait. Do you have an electrical meter? You also said "main" board. Is there a separate time delay relay or sequencers?0