Side arm
SeanBeans
Member Posts: 525
What are some side effects of having one pump for both, an indirect and 2 zones of heating.
Pump would be mounted on side of boiler pumping into return tapping.
TIA
TIA
OK I'm confused. Is this a hot water boiler? Or are we running a couple of zones and the indirect off a steam boiler?
Either way you could use one pump and appropriate valves, but if this is a steam boiler and you are pumping into the return rather than a closed system, you are guaranteed to have cavitation problems on that pump.Br. Jamie, osb
This is theoretical @Jamie Hall
It would be a hot water boiler with two zones of heating and one priority zone of DHW.0 -
This is done all the time. It does not work all that well with a mod/con and outdoor reset.SeanBeans said:This is theoretical @Jamie Hall
With a cast iron boiler you can use one circ and pipe straight through the boiler, no primary/secondary."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
The only reason I would have a separate pump for an IDWH is in the case of a P/S setup. Take the loop for the IDWH off before the secondary loop, so as to direct pump the idwh off the boiler without having to pass through any P/S piping. In that case you would need check valves to keep the flow where you want it. In direct piped systems though, a zone valve and a priority control works just fine. make sure your zone valve Cv is high enough to get the required flow for the IDWH though..0
So in this photo is shows how the manufacturer recommends doing it..
Now imagine taking both of those pumps out and only putting on pumping into the boiler..
The reason for this question is that the books shows two circs in specific positions. but if we were to ignore their recommendations and whatever we wanted like a lot of installers seem to do.. what would happen?
Everything works the same?0 -
If you only put one pump pumping into the boiler, you will be effectively pumping towards the point of no pressure change assuming the expansion tank is where it is on the diagram.
As to using one pump for multiple zones and using zone valves instead of zone pumps, it will be fine as long as the pump has the capacity to pump the heating zones at the same time, and the indirect by itself (assuming a priority control is used).0 -
I might point out that the two diagrams are basically the same, just that with multiple heating zones, a reverse return piping system seems to be what they want. with a single heating zone and priority DHW reverse return is not necessary as they will never run together at the same time.0